Regarding Selection of PS Class Current Transformer

11/15/2011 6:20 AM

Dear,

Im using generator differential protection relay CAG-34 of Areva make for genset application (500 KVA DG Set )To order the current transformer of PS class i need to furnish details like Knee voltage Vk , Rct & Rl value.How do i can calculate all this value.i need the formula with example for genset application.Kindly forward all formula to find the values.fault current,constant for relay etc etc.

Regards,

sachin.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: Regarding Selection of PS Class Current Transformer

11/15/2011 8:22 AM
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Regarding Selection of PS Class Current Transformer

11/15/2011 8:32 AM

First of all, 500kVA Generator DOES NOT require differential protection. But, may be, your application is so critical that you don't mind the huge investment.

Well! KneePoint Voltage Vkp > K If(s) (RCT + 2 RL) ,

where, K = Constant of Cushion (generally taken as 2)

If(s) = System Fault Current as reflected on the secondary side of the CT

= Primary fault current / CT Ratio

Primary fault current = Generator Rated Full load current / Generators sub-transient

reactance

RCT = tobe given by the CT Manufacturer

RL = Two way resistance of the cable lead between the CT & the relay (this you should know as you only know the size and length of the cable you are going to provide)

Register to Reply Off Topic (Score 6)