11/18/2011 4:21 AM
We have a issue with our CAT 3406 camp generator. We have to replace AVR (CAT R448)by a new one( CAT VR6) as a part of fault finding/trouble shooting. While removing old AVR our electrician forgot to mark the exciter field wires(i.e. +ve or -ve). Wires have terminal markers but it is worn out.
Can anybody help me with test procedure to find out correct polarity of field wires.
Re: Exciter Field Terminal Polarity
11/18/2011 10:51 AM
Just hooking a voltage tester between the two wires and cranking the generator should identify pos and neg...If hooked correctly will register voltage if not then switch..
11/18/2011 10:28 PM
I am quite unsure about the wire condition which has come out, try adding a diode in any one of the terminals in forwards bias, only one combination should work.
Frank - Catch my statement if you can.
Good Answers: 102
11/19/2011 1:33 AM
It shouldn't matter if the flywheel diode is in the exciter controller. If this or any other polarity dependent protection is integral to the exciter field assembly then just buzz it out with an ohm meter. You want the diode to be normally reverse biased ie the correct polarity is not a short circuit across the fields.You want to see series resistance. You can work out for yourself which way the current flows on your ohm meter.