Low Fault Current Results in High Arc Flash

11/18/2011 10:02 AM

I need some help in understanding and possibly mitigating an issue that I have seen in several locations. It seems that every time I have low fault current available from the utility, I always end up with a category 4 or worse on the secondary side / line side of the breaker downstream. I'm not really sure what causes this or how to mitigate the issue. Any help is appreciated.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Low Fault Current Results in High Arc Flash

11/18/2011 11:01 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Low Fault Current Results in High Arc Flash

11/18/2011 1:48 PM

I you have a low fault current from the utility you should have a reduce fault on the secondary of the transformer. Is that your question?

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3

Re: Low Fault Current Results in High Arc Flash

11/18/2011 3:03 PM

One of the major contributing factors to the secondary side fault current is the size of the transformer feeding the system. You may have fairly low primary (utility) fault current, but if your transformer is pretty large, the transformer ratio is high, and/or it has a low % impedance, it can source a pretty hefty fault current at secondary voltage. A quick estimate for available secondary fault current (assuming infinite bus on primary), is to divide Full Load Amps (FLA) secondary by the impedance as a decimal. Try this with impedances of 5%, 8%, and 10% (.05, .08, .10), for example, and you will see the difference. Maybe it has to do with your choice of transformer. It is possible to specify higher % impedance from standard ANSI value to reduce fault currents (utilities do it all the time!), but you may pay some extra.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #3

Re: Low Fault Current Results in High Arc Flash

11/19/2011 12:29 AM

But, if the source fault level is low, that would surely reduce the secondary side fault current too. Isn't it?

Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#5

Re: Low Fault Current Results in High Arc Flash

11/19/2011 9:19 AM

The arc flash energy is greatly dependant on the speed of the protection.

In general, a low fault current will take longer to clear (by the protective device). While the arc energy will be lower, the exposure time will be longer. The combined effect can be that the cumulative emitted radiation is higher demanding a higher level of protection (high calories).

You can reduce the calorific level by selecting faster breakers and/or tightening the coordination levels.

Using protections that are fast and current limiting can also make a big difference.

At the extreme, try a semiconductor rated fuse (or a very fast one). The extreme speed will bring the calories down quickly. It might be difficult to coordinate with other protections though, but that is another problem...

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#6

Re: Low Fault Current Results in High Arc Flash

11/19/2011 6:30 PM

Marcot has the explaination to the OP's question. If you choose and infinite bus to get your fault value you can get in trouble Example

Transformer 1500 kVA 3.5%z 208 VOLTS

Infinite Bus = 118 ka

5000 amps available primary = 85 ka

1000 amps available primary = 40 ka

Extreme examples but it shows the difference when you use available fault values.

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers: