30kw Induction Motor Run In Star Continuously

11/18/2011 12:36 PM

I have a 30 KW Induction motor driving cooling tower fan.

The fuses and the main contactor of the DOL starter are rated at 100A.

But, the main contactor was melted out completely while starting the motor.

What may be the reason..?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster #1
#1

Re: 30kw Induction Motor Run In Star Continuously

11/18/2011 12:57 PM

Rated Voltage/ Current? Looks to be 40A around in that case for the DOL the starting current would be much more than the 100A and that may be the reason.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: 30kw Induction Motor Run In Star Continuously

11/18/2011 12:58 PM

Hard to understand what you are referring to. DOL starter, main contactor? What's the difference? What does running in Star have to do with this?

Let's start over.

You have a 30kW motor. What's the nameplate data for it?

What is your line voltage"

What kind of starter to you have, DOL? Star-Delta? Something else?

How have you wired it up, as in what kind of conductors and what size did you use?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Participant

Join Date: Nov 2011
Posts: 2
#8
In reply to #2

Re: 30kw Induction Motor Run In Star Continuously

11/20/2011 5:00 AM

The Motor is running since so many years might be 30 years. Earlier it was run with rotor resistance starter and 10 years back it was connected to DOL starter in a feeder of L&T make panel MCC with 415 volts line voltage. Since then also it was working very well. But recently, Feeder's main contactor melted out while starting.

The motor terminals u2, v2, w2 are permanantly shorted with links and u1, v1, w1 are connected to the feeder with line voltage 415v.

I checked the cable for damage but its ok. not damaged. Checked the motor winding and it also found ok.

I Changed the contactor with new one and started the motor. It is running well. The starting currentwhen checked with clamp meter was going upto 140Amps, and coming back to 25 amps for continuous run and I run it for 10 hours. No problems found till.

But the contactor is getting heated up. Don't know whether this one also fail or not?

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#9
In reply to #8

Re: 30kw Induction Motor Run In Star Continuously

11/20/2011 9:56 AM

"earlier it was running with rotor resistance starter"

Now, you have started confusing everybody. Does this mean that the motor is a Slip Ring Induction Motor?

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#10
In reply to #9

Re: 30kw Induction Motor Run In Star Continuously

11/20/2011 11:46 AM

Yes, curiouser and curiouser. Are you sure it was a ROTOR resistance starter, or was it a Primary Resistance Starter? If it is a Wound Rotor Induction Motor and you have the slip rings shorted out, the starting current will be extra high, much higher than a standard contactor that is rated for thie running current can handle. A typical induction motor will draw 600% current on startup and contractors with motor ratings are made to handle that. But a WRIM with shorted slip rings can draw upwards of 1000% starting current, much more than the contactor is designed for. if you meant a Primary Resistance Starter used on a standard induction motor, that's a different animal.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: 30kw Induction Motor Run In Star Continuously

11/18/2011 1:06 PM

I would check the wiring voltages to make sure your delta leg is properly located...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: 30kw Induction Motor Run In Star Continuously

11/19/2011 12:27 AM

Are you sure? 30kW motor connected in star and running with DOL? I very much doubt.

Register to Reply
Anonymous Poster #1
#5
In reply to #4

Re: 30kw Induction Motor Run In Star Continuously

11/19/2011 1:35 AM

Permanent star mode- that means the motor might be oversized for the application

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6
In reply to #5

Re: 30kw Induction Motor Run In Star Continuously

11/19/2011 10:16 AM

Without answers to my questions we don't know what this means. Some motors are designed to be connected in Star for one voltage, Delta for another. Speculating without proper data can result in people going off and doing things they should not be doing.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#7
In reply to #6

Re: 30kw Induction Motor Run In Star Continuously

11/19/2011 11:10 AM

I agree...What are your voltage readings. Was the starter new and destroyed in a single attempt to start, or over the course of time, how much...Is the motor wired in star,or do you have a high leg and wired in delta...Does the fan turn freely, is it belt drive, is the belt adjusted properly, are the bearings good...What is the amp draw on start-up, and after start...Have you done any diagnostics on the motor, what were your readings..

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11

Re: 30kw Induction Motor Run In Star Continuously

11/21/2011 3:21 AM

One possibility is that the contactor closed onto a short-circuit. It's difficult to see from here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply