Short Circuit Current for Sychrinized DG Set.

11/19/2011 6:33 AM

We have 6 generators each of 2000 kVA, 415 volt and will run in synchronizing. The value of direct axis sub transient reactant is 13%. According to this the value of fault current on bus will come approx (21*6 =126 Ka). So we need a 125 Ka breaker and a bus or can we use circuit breaker with low breaking capacity and high speed tripping relays?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Short Circuit Current for Sychrinized DG Set.

11/19/2011 11:06 AM

NO! The Circuit Breaker HAS to have a capacity of more than 126kA for SURE. You should be looking at 150kA CBs. These will be current-limiting breakers and will act much before any relay can act, however rapid the relays are. This is known as 'reflex trip'....quite similar to what happens in the human body.

Please study the catalogs of top switchgear companies to learn more about rapid-trip circuit breakers.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Short Circuit Current for Sychrinized DG Set.

11/19/2011 10:27 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Short Circuit Current for Sychrinized DG Set.

11/20/2011 10:04 AM

Go for solution given by KVS! Alternately, you can go for current limiting reactors to limit the fault current to less than that of the CB breaking capacity. But, then be careful about voltage drop in the reactors.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#4

Re: Short Circuit Current for Sychrinized DG Set.

11/20/2011 10:59 AM

Ampilfying my post a little, here is an oscillogram collection from LS Industrial Systems, whose Susol MCCBs (based on the rotary double-break design pioneered by Schneider Electric) are one of the fastest CBs in the world....1.3 milliseconds of clearing time on a prosepctive 150kA !!! (Please note the peak current let through)

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Register to Reply 4 comments