Voltage and Reactive Power Hunting Show in My Power Plant.what Reason Behind

11/19/2011 9:08 AM
I'm working in 16 MW ,11 kv, three STG power plant. All three are running parallel. suddenly voltage and reactive power hunting started,all three machine, I also search if AVR or any motor ya other equipment responsible for this hunting, but no result found till date, please suggestion me. yesterday night i doing duty in STG panel desk,my three STG operating 9 ,10,8 mw, 5,6,3 mvar,10.71,10.72,10.72 kv,50.10,50.20,50.05 Hz, reactive hunting all three m/c and shifted just like it, 8,2,4 mvar, voltage also, 10.65 kv dropped.then some time after 3,9,2 mvar,.if u have experience this type of problem .so give solution. all three STG are identically, no grid connected,.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Participant

Join Date: Mar 2009
Posts: 4
#1

Re: Voltage and Reactive Power Hunting Show in My Power Plant.what Reason Behind

11/19/2011 12:56 PM

As mentioned,if grid connectivity is not there, the inflencing factor for a change in reactive power only would be terminal voltage controller (AVR). With 3 units running in parallel, voltage drop would be dependant on their individual AVR droop settings.

Please confirm that there is no change in load (MW) requirement.

1.Check for individual response & settings of AVR. Normally should be same.

2. Load sharing review is required, as is evident, by data given , unit no:2 acts as master (50.2 hz), and causes the other two to " follow".

3. Response of Controller valves of STGs for similar inputs needs to be checked.

Register to Reply
Active Contributor

Join Date: Jan 2010
Posts: 19
#4
In reply to #1

Re: Voltage and Reactive Power Hunting Show in My Power Plant.what Reason Behind

11/28/2011 10:19 AM

sir,

no change in load,

TG model no.TGP221240/2

AVR TYPE. EX173166/4 both BHEL make.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Voltage and Reactive Power Hunting Show in My Power Plant.what Reason Behind

11/19/2011 5:06 PM

See thread http://cr4.globalspec.com/thread/73608 This the second time you've asked the question!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#3

Re: Voltage and Reactive Power Hunting Show in My Power Plant.what Reason Behind

11/20/2011 12:54 AM

Please put some understanding into it. The different frequency reading are impossible as frequency. They indicate phase variation and hunting around a common center value. Your regulator's setting are impossibly tight. Nor do I see any dead band where there is no regulation at all. Relax the settings to more reasonable values. Allow a % or 2 before regulation kicks in. Allow one gen be the first to pick up load. It cannot hunt against itself. Etc, etc.

Relax yourself, relax them. And report back in a few weeks, that most likely all your problems disappeared.

Register to Reply