Changing Options of Underloaded 160kw Motor?

11/20/2011 6:51 AM

In our company there is 160 kw motor running with star delta starter. Running load is 90A Pf .85 Voltage 426v Can I change this vaccum pump motor with 110kw motor.. Please guide dear friends......

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Changing Options of Underloaded 160kw Motor?

11/20/2011 8:17 AM

It would seem to be over rated, but does it have any peak loads it has to handle?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Participant

Join Date: Nov 2011
Posts: 4
#2
In reply to #1

Re: Changing Options of Underloaded 160kw Motor?

11/20/2011 9:15 AM

no peak loads. Main motive is energy saving by smaller rating motor.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3
In reply to #2

Re: Changing Options of Underloaded 160kw Motor?

11/20/2011 10:00 AM

But then why did they select a 160kW motor? Cushioning?

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Changing Options of Underloaded 160kw Motor?

11/20/2011 11:07 AM

Motors use only what they need to use, plus losses inside the motor. All you will save is the very slight difference in the losses, maybe a fraction of a percent of total consumption. The cost of the new motor must be compared to the energy savings in order to properly evaluate this. If it runs 24/7/365 it may be worth it, but if it runs intermittently, as vacuum pumps often do, the payback may be too long to be of immediate impact.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Participant

Join Date: Nov 2011
Posts: 4
#7
In reply to #4

Re: Changing Options of Underloaded 160kw Motor?

11/21/2011 3:37 AM

yes its running 24/7/365

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#5

Re: Changing Options of Underloaded 160kw Motor?

11/20/2011 11:59 PM

The smaller motor will run hotter and not save any energy.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#6

Re: Changing Options of Underloaded 160kw Motor?

11/21/2011 2:34 AM

They say at about 80% of the rated load the efficiency is maximum,so select accordingly

__________________
pnaban
Register to Reply
Anonymous Poster #1
#8

Re: Changing Options of Underloaded 160kw Motor?

11/21/2011 8:20 AM

In India at 415 V (how did you manage 426V?) 3 phase

The power consumption is sqrt(3)x415x90x0.85 = 55KW and even at 426V(?) is 56KW

At 165KW you are running the motor at approximately 33% Load. At this load though the efficiency could be a few percentage lower but I won't have expected a high 0.85 pf. A pf of 0.65 to 0.7 would have been more probable.

The basic question is still why this very highty overrated motor?

Though I am not much aware of the vacuum pump characteristic curves, may be under certain load conditions it might need that power.