Current Transformer Rating

11/20/2011 7:12 AM

Good day every one. Wanna ask what does 400-200/1 A rating of the current transformer mean actually. We are using this in transformer differential protection application.

Best Regards,

AJ

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: Current Transformer Rating

11/20/2011 9:36 AM

The primary side of the CT has two coils (generally single turn coil) which have the option to be connected in series or parallel. For the primary coils are connected in series, the CT ratio is 200/1A and they are connected in parallel, the CT ratio is 400/1. The CT nameplate should have connection diagram for both options. Generally this sort of CT is supplied with the two pieces of connection splice for the connection.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Current Transformer Rating

11/20/2011 9:59 AM

It will be a multi-tap CT ( a dual tap). The seconday winding will have 'n' number of turns and at n/2 turns, there will be a tapping for external connection. Let us say, the secondary terminals are marked S1, S2 & S3; then Terminals S1 & S2 mean that the CT is 200/1A & Terminals S1 & S3 mean that the CT is 400/1A.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Nov 2011
Posts: 2
#3

Re: Current Transformer Rating

11/22/2011 9:08 AM

We can use it as a 400/1 A ratio or 200/1A also as per our requirement

Register to Reply Off Topic (Score 5)
Participant

Join Date: Oct 2011
Posts: 3
#4
In reply to #3

Re: Current Transformer Rating

11/24/2011 8:46 AM

Thank you all for your replies

Register to Reply Off Topic (Score 5)
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

a.jandhyala (1); electricalexpert65 (1); msamad (1); murugavelt (1)

Previous in Forum: Changing Options of Underloaded 160kw Motor?   Next in Forum: Pioneer Turntable Speed Problems

Advertisement