Trip Circuit Supervision

11/27/2011 12:45 PM

why trip circuit supervision is taking through breaker contact? what happen if take directly?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Trip circuit supervision

11/27/2011 1:06 PM

If your referring to the shunt trip it's to stop the coil being powered up unnecessarily once it's done it's job.

__________________
The reports of my death are greatly exaggerated.
Reply Good Answer (Score 2)
Active Contributor

Join Date: Mar 2011
Location: INDIA
Posts: 10
#2

Re: Trip Circuit Supervision

11/28/2011 9:30 AM

Basically trip circuit supervision is to supervise the tripping coil of a breaker, Some breaker may contain 2 or 1 tripping coil depending upon the customer requirements and the factor of safety. Hence the positive of the TCS relay will directly go to the relay coil and the negative will be sent through breaker tripping coil, which supervises the healthiness of the coil.

Reply Off Topic (Score 6)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Trip Circuit Supervision

11/29/2011 4:35 AM

To ensure that the breaker trip circuit is monitored both in pre-close as well as post-close conditions of the breaker.

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#4

Re: Trip Circuit Supervision

11/29/2011 8:04 PM

If you mean... why is it wired like below..

It is because the test current [through TCS] goes through all the contact wiring as well as the trip coil, checking the continuity of the whole circuit - not just the trip coil - which is why it is called "Trip CIRCUIT Supervision" (TCS), not "Trip Coil Supervision". Some protection relays have two terminals for positive etc, so that supervision covers internal wiring and automatically causes a supervision alarm if the relay is unplugged.

If you put TCS directly across the contact on the left (take directly??) then TCS would only check the coil and not the contact wiring.

I have left out additional coils and circuits of some "96" supervision relays which stop a supervision alarm occurring when the contacts stay closed, shorting out TCS, or which monitor trip coil while it is tripped (the trip coil often has a "built-in" contact, called a "cut-throat contact" which stops it being permanently energized in the tripped state, if the coil is not continuously rated).

Reply
Active Contributor

Join Date: Jul 2011
Posts: 13
#5
In reply to #4

Re: Trip Circuit Supervision

01/26/2012 3:41 AM

Thank you so much.. i was in doubt with this topic for so many days.. am now clear. here we are checking the status of breaker contact also through which trip comand is going.

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#6
In reply to #5

Re: Trip Circuit Supervision

01/26/2012 5:03 AM

Thank you for acknowledging our help.

Regards,

67model

Reply
Reply to Forum Thread 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

67model (2); chandru1982b4u (1); electricalexpert65 (1); javadkv (1); TonyS (1)

Previous in Forum: Frequency Rating for ULE (Universal Lite Engine)   Next in Forum: DC Supply-Current Status

Advertisement