Delta Testing of Power Transformer

12/04/2011 8:58 AM

I need to know that how much current injected in delta testing of power transformer.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: delta testing of power transformer

12/04/2011 9:07 AM

Why do you need to know? And why do you not already know?

Why do you not consult the governing specification documents that control such tests?

delta testing of power transformer

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Delta Testing of Power Transformer

12/04/2011 11:05 AM

The answer is 42.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
3
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#3

Re: Delta Testing of Power Transformer

12/04/2011 3:30 PM

IEC 60250 gives everything required to be known about tan delta test. The basic knowledge should be an understanding of tan delta. If you know that everything is clear.A pure insulating material act as a capacitance. The current will be 90 degree ahead of voltage. Depending on the impurity there will be a resistive component resulting an angle and the tangent of the angle gives the degree of contamination in the insulating materiel which is measured and IEC stipulate a safe limit value of the insulation which is considered acceptance level

Register to Reply Good Answer (Score 3)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Delta Testing of Power Transformer

12/05/2011 3:33 AM

RTFM.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply