Anonymous Poster #1

ELR Tripped When Switching on the 3 Phase 60kVA Isolation Transformer

12/05/2011 5:04 AM

my client is having a problem when switching on the 3 phase 60kVA isolation transformer whereby the Earth Leakage Relay (ELR) trips. the setting of the ELR is 3A and the delay timer is set to maximum. there is no such problem with the 150kVA transformer. is it due to the inrush current that causes the leakage current to increase...? please advice.

thank you.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: ELR tripped when switching on the 3 phase 60kVA isolation transformer

12/05/2011 5:06 AM

<...is it due to the inrush current that causes the leakage current to increase...>

No. It's due to the earth leak fault that is not related to the inrush current.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Member

Join Date: Jun 2011
Posts: 7
#3
In reply to #1

Re: ELR tripped when switching on the 3 phase 60kVA isolation transformer

12/05/2011 5:33 AM

sorry for not being clear earlier. the tripping does not occur everytime but very frequent when switching on the transformer. once the ELR passes through this stage, the transformer runs perfectly. therefore, i think this leakage current that causes the ELR to trip is not real value but emplified...some how...?

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: ELR tripped when switching on the 3 phase 60kVA isolation transformer

12/05/2011 5:39 AM

It's all just speculation until the insulation tester advocated in reply #2 has been put to work. Why not look for the actual problem and then correct it?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#2

Re: ELR tripped when switching on the 3 phase 60kVA isolation transformer

12/05/2011 5:27 AM

Measure the insulation resistance (phase to earth) with a Megger tester (or similar) and report results.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Member

Join Date: Jun 2011
Posts: 7
#5
In reply to #2

Re: ELR tripped when switching on the 3 phase 60kVA isolation transformer

12/05/2011 5:39 AM

it's 352Mohm

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: ELR tripped when switching on the 3 phase 60kVA isolation transformer

12/05/2011 5:52 AM

What is the insulation resistance of the wiring connected downstream of the ELR?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7

Re: ELR Tripped When Switching on the 3 Phase 60kVA Isolation Transformer

12/05/2011 9:15 AM

Is it anumerical type ELR?

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#8

Re: ELR Tripped When Switching on the 3 Phase 60kVA Isolation Transformer

12/05/2011 5:54 PM

You have not told us..

  1. Transfo primary voltage.
  2. Number and circuit positions of CT connected to relay.
  3. Current transformer [CT] ratios.
  4. Time delay setting.
  5. Is this a new installation or one which used to work OK?

Without this, we have little idea of the significance of 3 amp setting.

How do the settings compare with those for 150 kVA transfo?

What are CT details for 150 kVA transfo?

Are primary voltage and relays same for both transfo? If relays are same, have you tried interchange (with change of settings, of course)? Or secondary injection test of relay?

Inrush (magnetizing) currents are never symmetrical between phases - this causes problems with the matching of the CTs [the CTs themselves have different saturation at switch-on] - and sets a lower limit to how low the earth fault setting current/time delay can be.

It does not seem like a real fault - it seems like a wrong setting or relay or CT problem..

Reply
Member

Join Date: Jun 2011
Posts: 7
#9
In reply to #8

Re: ELR Tripped When Switching on the 3 Phase 60kVA Isolation Transformer

12/05/2011 8:22 PM
  1. the primary voltage of the transformer is 415V
  2. there are 2 ELR incorporated into the system 1 before the transformer and the other one after the transformer.
  3. ELR uses single zero sequence current transformer.
  4. time delay setting is 3s
  5. this is a new installation.
  6. both transformers are set similarly.
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#10
In reply to #9

Re: ELR Tripped When Switching on the 3 Phase 60kVA Isolation Transformer

12/09/2011 7:35 AM

It seems you are using a "core balance" CT. In this, all 3 phase cables pass through one CT. I guess same CT type may be used for both transfo, in that case, the smaller cables may be a loose fit.

This kind of CT avoids problems of CT balance, but perfect balance is only got if the cables are disposed symetrically about the CT centre and pass perpendicular to its plane - within CT and for some distance outside it.

Is it possible the cables are badly aligned? Have you checked against CT maker's requirements? Have you asked CT maker for help - they will have test experience of what CT "earth fault" current settings are practical for this CT and how much cable alignment affects operation.

I suggest

  1. Open transfo input Isolator.
  2. Check all transfo phases dead with voltmeter.
  3. Short all cables together at transfo input.
  4. Apply voltage to CT secondary with Variac, be sure transfo is not saturated (e.g. doubling test voltage only doubles CT current).
  5. measure and record voltages between phases at isolator caused by CT field.

Ideally, voltages at 5/ are identical.

Do test on 150 kVA transfo also, for comparison.

Can you do a primary current injection into each CT primary cable, to check relay setting? A current of 3 amps is not much to get using Variac/step-down transfo and resistor or lamp ballast e.g. 240/12 V transfo with motor car headlamp bulb.

Reply
Commentator

Join Date: May 2011
Posts: 84
Good Answers: 1
#11

Re: ELR Tripped When Switching on the 3 Phase 60kVA Isolation Transformer

12/10/2011 3:16 PM

insrush current when making on a transformer may trip the ELR connected to it.

residual inrush current in 3 phases as seen by CBCT may be greater than 3A, thats why ELR trips.

This difference is due to inductance of transformer windings. Ensure proper useage of stabilizing resistors in case you use CBCT with ELR or Numerical relays with 3 CT's wiring inputs.

Reply