Section 4.5, AS3008 - Voltage DropBased on Load Power Factor

12/07/2011 10:56 PM

Hi guys,

I was reading through AS3008 the other day when I stumbled across this:

4.5 DETERMINATION OF VOLTAGE DROP FROM LOAD POWER FACTOR

It talks about how if the load power factor is different from the cable power factor, then different formulas are used (from the conventional Vd=sqrt(3)*I*Z or Vd=2*I*Z).

In what cases will the load power factor differ from the cable power factor? Is this only for very long cables? Can someone please explain how they would differ?

Thanks

__________________
Electrical Engineer
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Participant

Join Date: Mar 2011
Location: Vietnam
Posts: 2
#1

Re: Section 4.5, AS3008 - Voltage drop based on load power factor

12/08/2011 1:32 AM

Yes, the load power factor does affect voltage drop, but the formulas are used for 2 cases: 3 phases then Vd=sqrt(3)*I*Z, one phase then Vd=2*I*Z

Why it is related to load power factor, it is because Z=R*cos(phi)+X*sin(phi), cos(phi) is the power factor so that is why.

One last thing, there is no definition of cable power factor. You just need to care about the power factor of the load it connects to.

Regards,

P.

Register to Reply
Commentator

Join Date: Jul 2010
Posts: 92
Good Answers: 1
#2
In reply to #1

Re: Section 4.5, AS3008 - Voltage drop based on load power factor

12/08/2011 1:48 AM

How come in section 4.3.1 and I quote:

"Voltage drop in a circuit represents the vectorial difference in voltage between the origin or supply end and the load end. For the purpose of determining the maximum voltage drop value in Clause 4.2, the voltage drop (Vd) has been related to the impedance of the cables forming the circuit when the power factor of the cable is equal to the power factor of the load, in which case-

Vd = IZc

Zc = impedance of cable, in ohms

= √(R2c + X2c)

"

?

__________________
Electrical Engineer
Register to Reply
Participant

Join Date: Mar 2011
Location: Vietnam
Posts: 2
#3
In reply to #2

Re: Section 4.5, AS3008 - Voltage drop based on load power factor

12/08/2011 2:11 AM

Ah, it is beyond my knowledge, sorry. It is my mistake about Z=R*cos(phi)+X*sin(phi)

The formulas are stated that : Vd=sqrt(3)*I*(R*cos(phi)+X*sin(phi)) or Vd=2*I*(R*cos(phi)+X*sin(phi)), so I jump to conclusion that Z=R*cos(phi)+X*sin(phi)

It is true that Z=R*cos(beta)+X*sin(beta) and cos(beta) is not usually equal to cos(phi). (I checked that before)

but to call that power factor of cable is quite new to me.

To my understanding, voltage drop is applied when the current (of the load) run through the cable (with impedance) and loses an amount of power (sqrt(3)*U*I) and the voltage reach the end will be lower or higher (depends on L or C of cable), usually lower and calculated as above formulas.

The words quoted may say it in an academical way. :)

Sorry if no helping for you.

Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#4

Re: Section 4.5, AS3008 - Voltage DropBased on Load Power Factor

12/09/2011 10:16 AM

To maximize power transfer, output and input impedances must be balanced at all times. To maintain this balance in impedance and power factors both for output (load) and input (source), the load must always be maintained balanced for all 3-phases. Once some loads were taken off line, a corresponding load imbalance is created which will be reflected with a corresponding voltage changes on the supply line as this is also is reflected as a change in the original power factor of your load, etc.

Hope this helps..

__________________
vsar
Register to Reply
Commentator

Join Date: Jul 2010
Posts: 92
Good Answers: 1
#5
In reply to #4

Re: Section 4.5, AS3008 - Voltage DropBased on Load Power Factor

12/12/2011 2:17 AM

When you have imbalanced phases, this does not change the load and supply power factors. It merely means either your phase voltages change. Current and voltage at the supply side will be of the same angle difference at the load side afaik.

__________________
Electrical Engineer
Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#7
In reply to #5

Re: Section 4.5, AS3008 - Voltage DropBased on Load Power Factor

12/12/2011 7:47 AM

Don't you effectively change your load impedance when a load imbalance is created?

__________________
vsar
Register to Reply
Commentator

Join Date: Jul 2010
Posts: 92
Good Answers: 1
#6

Re: Section 4.5, AS3008 - Voltage DropBased on Load Power Factor

12/12/2011 2:17 AM

Someone has to know the answer!!

__________________
Electrical Engineer
Register to Reply