Dear gurus,

During commissioning, we have a differential earth fault trip in our 3 phase heater with SCR control.

690V 100kW and connected in Delta. Differential earth fault setting is 300mA and 0.4second. The SCR is controlled 2 phase only (U, V) and W is direct connected to L3.

1. Is it okay to use SCR in 2 phases only? It can create current unbalance?

2. Delta connection is ok? Because we experience heating also

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Trouble on 3 phase heater with SCR control

12/11/2011 5:28 AM

Wow! That must have been engineered by some of the poster children here on CR4.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Trouble on 3 phase heater with SCR control

12/11/2011 1:13 PM

Check to see if someone configured your heater elements in a Y and then grounded the Neutral on it...

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply Score 1 for Good Answer
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#3
In reply to #2

Re: Trouble on 3 phase heater with SCR control

12/11/2011 10:23 PM

Agree. Correct wiring is the first thing to look at. Then highpot the heaters.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Reply
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#4

Re: Trouble with 3 Phase Heater with SCR Control

12/11/2011 11:05 PM

There is nothing wrong with SCR & delta connected heater load. First we have to find the reason for tripping. Can you just test SCR pack on about 5% dummy known completely isolated load and check whether still the system it trips?

__________________
Subramanyam
Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: Trouble with 3 Phase Heater with SCR Control

12/12/2011 12:06 AM

It is perfectly normal to do SCR control on 2 of the 3 phases, it is a way to save money on the SCR controller because you only need 4 SCRs instead of 6. There are however two major caveats to doing that:

1) It can only be done on UNGROUNDED 3 phase heater element gonfigurations. They can be wye or delta, but if wye (star) it cannot be a 4 wire connection of the elements, i.e. where the wye (star) connection point is connected to the grounded neutral of the power distribution system.

2) It DOES create a phase current imbalance. Were the load a motor this would be a problem but it is a heater, so no problem for the load. However one thing you can't do is differential (residual) earth fault protection on it as it is INTENTIONALLY imbalanced. So you have two choices: remove the earth fault protection, or if that is not possible, change to a full 3 phase controller (6 SCRs).

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 3)
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6

Re: Trouble with 3 Phase Heater with SCR Control

12/13/2011 12:07 AM

What type of elements are these?

Are you heating air or water or something else?

Have you tried increasing the Differential earth fault setting to a higher current to see if the "problem" "goes away"?

Is the diff earth fault device legacy or part of the new installation?

You are commissioning. Now is the time to mess with these things.

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Reply to Forum Thread 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

JRaef (1); kvsubramanyam (1); marcot (1); SolarEagle (1); Tornado (1); Wal (1)

Previous in Forum: AVK Alternator Problem   Next in Forum: Battery Or Charger Problems

Advertisement