Interference Between Power and Instrument Cables

12/12/2011 7:28 AM

How it can get the Interference between the Power and Instrument Cables?

What is the reason for Interference for cables?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Interference

12/12/2011 7:35 AM

Don't shield or separate the conductors. That'll give you plenty of interference.

Cross talk, poor shielding or lack of separation.

I hope you're not taking a test.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Interference

12/12/2011 7:54 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#3

Re: Interference Between Power and Instrument Cables

12/12/2011 3:15 PM

The "reason" for interference would be improper cable selection by an inexperienced designer.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Interference Between Power and Instrument Cables

12/13/2011 7:45 AM

You must have studied something called "proximity effecet". Whenever a conductor carries a current, a magnetic field (flux) is et up around the conductor. This flux will cut any nearby conductor and as per the famous Faraday's law, will induce an EMF in the nearby conductor (provided that it is an alternating flux). If the nearby conductor has a closed path, then there will be an induced current flow due to this induced EMF. This induced current will interfere with the original current that was/is flowing in the nearby conductor. This is particularly problematic, if the nearby conductor happens to be the part of an Instrumentation Signal cable, wherein the signal is alreday very weak; the interference thus causing data errors or worse.

Register to Reply Score 1 for Good Answer
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); lyn (1); SolarEagle (1); WJMFIRE (1)

Previous in Forum: Stability Test   Next in Forum: Transformer Capacity

Advertisement