Transformer Capacity

12/12/2011 11:02 AM

We have totally 50 motors and total hp of all motors is 352 and tranformer is 250 kva. How to calculate the capacity of this trasformer

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Transformer capacity

12/12/2011 11:05 AM

The capacity of the transformer is stated in the original post: 250kVa. No calculation is necessary.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Transformer Capacity

12/12/2011 2:25 PM

You're overloading the transformer!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#3

Re: Transformer Capacity

12/12/2011 3:11 PM

746 watts x 352 hp = 261.1 kw. See any issues here?

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4

Re: Transformer Capacity

12/12/2011 4:53 PM

261 wk/0.80 pf = 326 kva. Any issues here? However the op did not say that all the motors ran at the same time.

Register to Reply
4
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#5

Re: Transformer Capacity

12/12/2011 7:20 PM

You didn't provide enough information. As already indicated, you didn't mention the diversity of the motor loads, largest motor size, motor starting method, future expansion etc. In the case of the possibility of running all the motors simultaneously, your transformer is undersize for sure. In addition to the running loads, you also must consider the starting of your largest motor and its starting method. Make sure your transformer's reserve capacity is at least 4 to 5 times more than the largest motor's kva.

For example, out of the 50 motors, consider one is 10 hp (7.5 kw, 460V) and all of the motors may simultaneously run. Assuming motor's p.f is 0.8, the kva size of the 10 hp motor is 7.5/0.8 = 9.3. In this case, total simultaneous running load is 352 x 0.746 / 0.8 = 328 kva. So, the minimum size of the transformer capacity is: 328 + 5 x 9.3 = 375 kva.

The transformer also should have the reserve capacity.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 4)
Participant

Join Date: Dec 2011
Location: chennai
Posts: 4
#6

Re: Transformer Capacity

12/12/2011 11:28 PM

Dear Susheel,

Please take the diversity factor into consideration apart from the parameters mentioned by other. It is dependent on the type of industry.

A rule of thumb is 2. that is . You can load the transformer 2 times of its connected load.

Regards,

Anand Purushothaman.

__________________
anandcumi@gmail.com
Register to Reply Score 1 for Off Topic
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7

Re: Transformer Capacity

12/12/2011 11:47 PM

Guesswork is not recommended. Fix a datalogger/power recorder and from the graph of kVA you can judge the transformer size required.

__________________
pnaban
Register to Reply
Active Contributor

Join Date: Dec 2011
Posts: 11
#8

Re: Transformer Capacity

12/13/2011 1:37 AM

You are connected 352 hp.. But we dont know what is the maximum demand..if you are not using any starter, it takes around 6 to 8 times of load current.. So you cant start the multiples of motors at a time.. If you maintain unity powerfactor you can load upto 250 kw..

Register to Reply Off Topic (Score 5)
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

anand purushothaman (1); Magesh (1); msamad (1); pnaban (1); PWSlack (1); TonyS (1); wareagle (1); WJMFIRE (1)

Previous in Forum: Interference Between Power and Instrument Cables   Next in Forum: LED Meters Revisited

Advertisement