The generator is 1MW and is driven by an expander ( it is an induction generator) its excitation is from the network. To control the frequency the generator output is fed to the network through a VSCF drive( variable speed constant frquency). The power output from the generator is through single core armoured cables of 300sqmm - there are 3 cables running in trefoil. From the generator to the transformer where a stepdown transformer steps down the voltage from 3.3KV to 685V - from the transformer the output is fed to the VSCF unit. The distance between the generator and the transformer is 200M. The output from VSCF is fed to the network through a stepup transformer from 685V to 6.6kv again via single core armoured cables - three of them in trefoil. The armour was not earthed in both ends of the transformer and the generator. Recently we had all the three cables failed - there were all three melted with the amour at one point about 85M from the transformer - the cables were under the trench which was conctreted with the thickness of the concrete about 200mm. The generator is protected against earth fault - but the protection did not operate as expected because the armour was not earthed.
The question is why such a fault has occured - is this due to the fact that both ends of the armour were not earthed. If so how can this happen? My understanding is that there must have not been any induced circulating currents as the path was broken - the question of overheating does not therefore arise. Does any body have experience of such failures? Please help.