CT & PT

12/21/2011 12:21 PM

what is a difference between CT & PT (current transformer & potential transformer) and what are there uses.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: CT & PT

12/21/2011 12:22 PM

That's covered on page 238 of your text book.

Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#2

Re: CT & PT

12/21/2011 1:13 PM

This will get you half of the way there:

Link

CT's are pretty basic and much more common...you probably already know that.

Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#3

Re: CT & PT

12/22/2011 2:09 AM

a CT is spelt with a "C" and a PT is spelt with a "P", hope this helps!

__________________
The square root of nothing is what you make it!
Reply
Associate

Join Date: Sep 2008
Location: Located in Indiana
Posts: 33
Good Answers: 4
#4

Re: CT & PT

12/22/2011 8:04 AM

This is a very basic question and you did misuse the word "there" - should have been "their" but I suppose you deserve an answer. I have to assume you know what a transformer is or else this is a real waste of time. Current transformers change the current - usually they step it down. Potential transformers change the voltage - usually down. Lots of power equipment operates at too high of a voltage and with too much current (amps) for the control equipment or the metering equipment. CT's reduce the current and PT's reduce the voltage to levels that are acceptable for the controls or metering. This is a basic answer to a basic question and there are lots of potential answers to the current question.

Reply
Participant

Join Date: Dec 2011
Posts: 1
#6
In reply to #4

Re: CT & PT

12/30/2011 9:31 AM

Dear Mr. Jim,

thanks a lot for the answer.

Reply
Participant

Join Date: Jan 2007
Posts: 4
#5

Re: CT & PT

12/22/2011 12:32 PM

Current and voltage transformers are used to reduce high current and voltage to levels where they can be connected to instrumentation without damaging the instrumentation.

Current transformers ratio's are normally selected to reduce the current to 5 amps on the secondary when you have full load current on the primary side of the transformer. Example a 100:5 current transformer will provided 5 amps at the secondary when 100 amps is applied to the primary of the transformer. The ratio in this example is 20:1.

Voltage transformers ratio's are normally selected to provide 120 volts on the secondary when full voltage is applied to the primary. Example a 100:1 voltage transformer will have 120 volts on the secondary when 12kV is applied to the primary of a PT. The ratio in this example is 100:1.

The multiplier for the CT and VT selected above would be CTR X PTR= 20 X 100 = 2000. If the above CT and PT were connected to some type of intrument the reading of the instrument would be multiplied by 2000 to get the correct results.