hello to all

in our company we purchased new extrusion machine,which approximately draw 600A of power(415v 3phase 50 hz.

i am measured neutral to ground voltage without switch on the extruder breaker,it reads 0.6v which is almost acceptable.but when we switch on the breaker it comes 8-9 volts.

we traced that in that machine 4 servo motors r there,we disconnected them from drive and measure N to G then it was ok.when we connect 1 servo motor, N to G voltage increases 2volts.if we connect other again it increases 2 means total 4 volts like that.if i connect all 4 it comes 8 volts.what may be the problem? we tested servo earth to machine earth its okk. all r ABB made and they r telling that its grounding problem.but i was experience this first time please suggest what steps i should take to overcome this prob.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Jun 2009
Posts: 80
#1

Re: neutral to ground voltage

12/21/2011 1:15 PM

You have the voltages and the currents and so you can calculate the resistances, and also how much you need to lower the resistance to meet specs. E=IR.

Register to Reply
Associate

Join Date: Mar 2011
Posts: 48
#2
In reply to #1

Re: neutral to ground voltage

12/21/2011 1:20 PM

sir actually that 600A is full load I.this is happening when we just on the machne breaker and without starting machine.so servo also not in running mode .and this is new machine and just taking trial run on the machine

Register to Reply
4
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#3

Re: neutral to ground voltage

12/21/2011 1:40 PM

What you are reading is caused by harmonic distortion from the servo motor drive. If you use a power analyzer you will likely detect 11th and 13th harmonics due to the way the servo power supplies conducts current to replenish the capacitors.

There are several ways to deal with this situation:

1) Ignore it. Excess harmonic energy is dissipated as heat in the power source equipment.

2) Install harmonic filters on the line. Does the same thing but in the harmonic filter.

3) Install as new or replace existing step down transformers that feed from the same 415 VAC line with or using specially wound phase shifted transformers. This actually uses the harmonic energy and balances the pulsed consumption so that the primary frequency becomes 50 Hz again.

If you want to know more, try searching on Harmonic Distortion

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply Good Answer (Score 4)
Associate

Join Date: Mar 2011
Posts: 48
#4
In reply to #3

Re: neutral to ground voltage

12/21/2011 1:56 PM

noturordinaryjoe sir,

thank u for ur answer but again i want to ask u 1 thing,is that distortion do trouble in system communication? because we r facing prob in in that also

Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#5
In reply to #4

Re: neutral to ground voltage

12/21/2011 2:21 PM

The power distortion is not likely to be the cause of communication problems. Generally the communication issues come from the power lines being too close to the communication lines. This is a very common problem that people learn to appreciate once they solve it. If you are seeing the communication noise when the big drives are connected, it is probably due to magnetic linkage between cables.

Sometimes you can solve communication problems by using shielded cables or wires. If, however, you connect the shield at both ends of the cable then you have more noise instead of less. This makes for a condition called a ground loop. Always only connect only one end of a shield wire.

Remember that currents produce magnetic fields which can then be absorbed by communication lines and converted back to a current of the same frequency as the source. That magnetic field falls off at the rate of 1/r*r where r is the radial distance between conductors. Generally you should keep communication wires at least 25 cm from communication lines if they are running in parallel. If they must cross or come close, try to minimize the overlap.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#6
In reply to #4

Re: neutral to ground voltage

12/21/2011 5:41 PM

GA to NotUR...

As to the "distortion"...

Shielding bonded at each end should work for a high frequency (>300kHz) control circuit. Try adding a shunt capacitor at one end (if it's bi-directional you can experiment). You can also try using multipoint (equipotential) shielding along the entire length (but that may be cost-prohibitive). Using a toroid in conjunction with the shunt cap may increase the efficiency as well.

Measure your shield with your test equipment (spectrum analyzer) on a dedicated isolated ground circuit (to see the actual interference with harmonics). Your control circuits may have an isolated SMPS which is common for some control devices (VME is one). The combination of an isolated (from line) SMPS and improper shielding (for the application) may be causing your issues.

Register to Reply
Associate

Join Date: Oct 2011
Posts: 34
#7

Re: Neutral To Ground Voltage

12/22/2011 12:18 AM

1)check the winding resistance of motor for each individual phase - it should be same .

2)check the voltage of each phase which has been feeded to the motor-it should be same .

If in case of changes , due to unbalance , there might be a flow of voltage in neutral circuit .

this may be the reason why you are getting the 8-9 volt .

Register to Reply
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Neutral To Ground Voltage

12/22/2011 3:19 AM

Part of the neutral-to-ground voltage is the expression of the neutral current multiplied by the earth loop impedance. The neutral current is simply the vector sum of all the phase currents, and is there because there is at least one single phase load on the system

Why is there so much concern about it? A greater concern would be the absence of a neutral-to-ground voltage, as that would indicate that the equipment isn't earthed.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Anonymous Poster #1
#9

Re: Neutral To Ground Voltage

12/23/2011 6:12 AM

Certainly there will be electric current flow when you switch on ground breaker of the motor, this causes increase in voltage. What is the permissible neutral to ground voltage in your system? Possibly you should use bigger grounding cables and reduce resistance of ground cable to earth. Check also grounding current of each motor for possible excessive grounding current.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #9

Re: Neutral To Ground Voltage

01/04/2012 5:54 AM
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: