Knee Point Voltage

12/24/2011 5:33 AM

Sir,

How do I find out the knee point voltage of the ct's? Why it is required only for ref. and differential ct's? Please give me the formula for the calculation. What is the actual meaning of knee point voltage?

Thank you

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Knee Point Voltage

12/24/2011 8:33 AM

Start here, or find your text book:

Current transformer - Wikipedia, the free encyclopedia

You've asked 3 elementary questions in the last week.

Are you a student????

Are you a new technician?????

Why the sudden interest????

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#2

Re: Knee Point Voltage

12/24/2011 11:44 PM

Students with school holiday assignments......

Why can't they get a holiday job and ask their mentor these questions?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Power-User

Join Date: Jun 2010
Location: Canada
Posts: 139
Good Answers: 6
#3

Re: Knee Point Voltage

12/25/2011 11:42 AM

I wonder why you are asking such elementary questions ? . . . when the answers are readily available on the internet already ? ?

Go to google and enter the appropriate key words . . . and there you are !

Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#4

Re: Knee Point Voltage

12/27/2011 4:55 AM

Knee Point:

(Magnetization characteristics of CT)

There are four regions. Knee point lies in Knee region of the excitation characteristic curve. It is defined as where a 10% increase in flux density causes 50% increase in exciting ampere-turns.

You may find the formula in the book.

As a rule of thumb (based on the above definition), knee point lies when the output mA doubles with the increase in increments of applied voltage. Hope that helps!

__________________
--
Register to Reply
Commentator

Join Date: Jan 2011
Location: India
Posts: 98
Good Answers: 2
#5

Re: Knee Point Voltage

12/28/2011 5:43 AM

Its not a rule to do KPV for REF, Diff CTs only. You can do for all CTs. People normally do this for PS class CTs bcoz they have very good KPV and serves special protection systems.

-Vijay

__________________
You don't understand anything until you learn it more than one way.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6

Re: Knee Point Voltage

12/29/2011 5:40 AM

Normally protection CTs like 5P, 10P or 15P are used in almost all protection schemes. But, for Unit Protection Schemes like Differential, REF, etc., these CTs are not preferred. Why?

In unit protection schemes, it is very very important that the scheme operates only and only for the internal faults and must remain stable for all external faults. That is, when the unit protection scheme operates, one can be pretty sure that something is wrong within the protected equipment.

Also, unit protection schemes are employed for very critical equipment in the network. As such, whenever any unit protection scheme operates, all hell breaks loose. And one cannot put back the equipment into service, without conducting an array of tests and ensuring that the equipment is fit to be put back to service. But, this will take time and effort. And until such time, the plant will be shut down.

So, it is all the more imperative that the unit protection scheme operates only for genuine internal faults and NOT for any external faults.

Now, if we employ conventional protection class CTs like 5P or 10P for this application, let us see what happens. Lets us assume that one has selected 5P10 Class CTs for a Unit Protection Scheme. Let us say, the relay setting is 10%; this means that any differential current of 10% will operate the relay. Now, a 5P10 CT means that the CT will maintain its accuracy at least up to 10 times the rated current. This means that the CT will not saturate at least up to 10 times the rated current.

This also means that the CT may saturate anywhere after 10 times its rated current. This level will differ for different CTs. Among the same two 5P10 Class CTs, one may saturate at 12 times and the other may saturate at 13.5 times. In such a condition, during a through fault condition, there will be differential current and the relay will operate for external faults too. Even when both CTs are identically manufactured, the deterioration of its core properties over time may differ and yet they may behave differently over time.

Also, even when the CTs may be supplying to unit protection scheme of the same equipment, it is highly impossible that all the CTs of the scheme will be located at the same place. The incoming side CTs or the outgoing side CTs may have to be located far away from the relay location, thereby incurring extended lead lengths, thus imposing additional burden on the CTs. This increased burden will also shift the saturation level, as we have already seen.

Thus again, during a through fault condition, there will be differential current and the relay will operate for external faults too.

There are many other similar factors contributing to the maloperation of unit protection schemes, when conventional protection class CTs are employed. Thus, it has called for a special class of CTs for such applications. That Special Class is called Class PS. (PS is the abbreviation of the French Word "Protection Speciale").

Here, instead of generalising on the minimum saturation level of the CT, the users have to exactly specify the saturation level of the CT. This is called the Knee Point Voltage (VKP), as it appears as a human-knee in the CT Magnetisation Characteristics. This specification will take into account the maximum through fault current, the actual lead burden, the relay burden & the resistance of the CT secondary winding, as also a factor of safety.

The minimum Knee Point Voltage for a given PS Class CT is calculated by:

VKP = K * I(f)s (RCT + RB),

where,

If(s) = Maximum thro fault current as reflected at the CT secondary terminals

= If(P) / CT Ratio)

RCT = CT Secondary Winding Resistance

RB = Connected Burden, includes the relay burden & the burden

of the connecting leads

K = Factor of Safety, normally taken as 2

VKP = Knee Point Voltage of the CT

As can be seen from the above formula, here the customer is specifying the level of saturation, duly taking into account the maximum possible fault current in his network, the actual burden connected to the CT, etc. If the factor of safety is taken as two, this means that at least up to two times the maximum possible fault current the CTs will not saturate. Which also means that at the maximum possible fault current, both the incoming and outgoing side CT characteristics would exactly coincide. That is, their secondary currents would match exactly and the scheme would not operate for any external fault.

Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#7
In reply to #6

Re: Knee Point Voltage

12/31/2011 9:47 AM

...and what about metering CT's???? :)

__________________
--
Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

abasins (2); electricalexpert65 (1); lyn (1); olehwi (1); vijaymail_electrical (1); Wal (1)