Difference Between MCCB and MCP (MPCB)

12/24/2011 5:26 AM

Sir,

There is major difference in physical appearance of MCCB and MCP (motor circuit protector) breaker without thermal protection, in one spec. The requirement is MCCB, but there is no type 2 co-ordination chart with manufacturer for the starters up to 15kw. MS question is can we call MCP as MCCB? Or are they technically both are same? Nowhere in the catalogue says its name as MCCB. Fault level and ratings meet with the requirements. are both the same or not?

Thank you

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Difference Between MCCB and MCP (MPCB)

12/24/2011 8:43 AM
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: Difference Between MCCB and MCP (MPCB)

12/24/2011 10:56 AM

As Lyn said elsewhere, you seem to have started trying to learn electrical engineering on CR4. Doable, will take a long time. (Btw lyn, how much for that crystal ball from LynDoor™ ?)

Specific to MPCB (Motor-protection Circuit Breaker)....you can study more HERE

1. It is phase-loss sensitive

2. It may be ambient compensated.

3. In lower sizes, the heater resistance restricts the fault current. >6 A or 10A, you need fuses to back up. These are not sophisticated current-limiting MCCBs.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Difference Between MCCB and MCP (MPCB)

12/24/2011 11:44 AM

The term "MCP" is not universally applied around the world, so it will depend on the context of where you are and/or who is reviewing your submittal.

Here in the US, an MCP is an MCCB with no thermal trips, for specific use in factory assembled, tested and listed combination motor starters where there is a separate thermal protective element, such as an overload relay. There is no other legal use for them, including field assembly or use in custom control panels. But the term MCP is actually a trademarked brand identifier of the old Westinghouse breakers, now owned by Eaton. So you will never see that term officially described in specifications. the "official" descriptor is an IT MCCB, for Instantaneous Trip Molded Case Circuit Breaker.

In IEC world, MCP has been unfortunately used to describe a different device, a motor protective device that has mag trips and adjustable thermal trips, essentially taking the place of the MCCB + TOL. This is the MPCB that KV mentioned above. In larger sizes these are Molded Case, but smaller ones are not.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Difference Between MCCB and MCP (MPCB)

12/29/2011 5:46 AM

MCCB: Moulded Case Circuit Breaker - having a thermal release & an instantaneous release and having very high short circuit breaking capacity. The thermal curve is not a very fine curve as to offer perfect protection to motor winding against overloads. They are deisgned to protect feeder cables.

MPCB: Motor Protection Circuit Breaker- having a thermal release & an instantaneopus release and having a limited short circuit breaking capacity. The thermal curve is the same as that of a bimetal overload relay, offering close protection to the motor winding against overloads.

Type-2 co-ordination charts are available both for MPCB + Contactor and MCCB + Contactor + External Thermal Overload Relay

Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); JRaef (1); kvsridhar (1); lyn (1)

Previous in Forum: Harmonics Impacts and Remedy   Next in Forum: Knee Point Voltage

Advertisement