Replacement of Electric Heater

12/27/2011 5:50 AM

We have 6 MW diesel engine. Nowadays our DG set is standby and runs only 2-3 hrs daily to control MD.

For jacket cooling of engine 30KW electric heater is being used and minimum water temperature required is 50 Deg C. Jacket cooling is done on slow rate to avoid thermal stressing .

Water flow rate is approx 8 m3/hr.

when engine runs heating is stopped automatically and if engine stops then heating started to maintain the jacket temperature.

please suggest any other source to heat water on slow rate for above application to cut electricity auxiliary consumption.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#1

Re: Replacement of Electric Heater

12/27/2011 11:13 AM

Here is a link

Here is more info

How about a magnet mount block heater?

How about a few of them?

At 200W each, you can assume there would be an electricity consumption savings over a 30KW heater even if you used 4 (4 - 2 each side of block)

You can also find heaters that are thermostatically controlled to turn off at a pre-set ambient temprature or operating temprature of the engine.

Disclaimer - I have been using a manual thermostat version of this heater on my home ge-set with success for 6 years.

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Replacement of Electric Heater

12/27/2011 2:35 PM

If the heater has a thermostat, it will cycle on and off as needed to keep the engine warm enough. If the heater is actually energized only 1/3 of the time, you could use a 10kw heater instead, running all the time. Total energy used would be the same, but peak power would be less.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster #1
#3

Re: Replacement of Electric Heater

12/27/2011 11:41 PM

Where are you located?

Pls evaluate the possibility of using SOLAR WATER HEATER for this application.

I am sure you can save a lot of energy and there are some excellant options available.

Register to Reply
Power-User
United States - Member - Member

Join Date: Dec 2006
Location: La Grande, Oregon U.S.A.
Posts: 468
Good Answers: 23
#4

Re: Replacement of Electric Heater

12/27/2011 11:46 PM

It seems a shame to have to supply heat to keep the water jacket warm during standby when you are throwing away so much heat while the generator is running. Consider storing some of that waste heat in a hot water tank, then using it to keep the water jacket warm. You can determine the hot water requirement by converting the electric heater KWh usage to BTU's. The controls would be similar to what you have now - a thermostatically controlled circulating pump.

__________________
Don't hit at all if it is honorably possible to avoid hitting; but never hit soft! - Theodore Roosevelt
Register to Reply
Commentator

Join Date: Jun 2011
Posts: 67
Good Answers: 2
#5

Re: Replacement of Electric Heater

12/28/2011 12:49 AM

Check with the manufacturer. I feel 50 Deg C temp. is too high. You will have considerable savings if the set point of thermostat was adjusted to say 35deg C. You may try a gas or diesel fired heater in an auxiliary heat exchanger for still more economy.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6

Re: Replacement of Electric Heater

12/28/2011 2:47 AM

For jacket cooling ?? You mean jacket heating so you can go straight to load from "cold" start up. Right?

The only way to escape parasitic consumption for heating is to harvest waste heat.

I don't know what type of facility this genset is serving. Are there any processes there that generate waste heat?

Naturally when the genset is running you will need to turn of the jacket heater. This could get complicated if performed with waste heat. The electrical heater is the simplest ergo most reliable way to achieve the required function.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply