Power Factor Controller L&T PFC-8

12/28/2011 7:28 AM

Sir,

I have automatic power factor controller with L&T PFC-8 controller. Presently the system is not working i mean not correcting power factor.I checked supply system and got no voltage at o/p points 1,2,3,4,5 & 6 of PFC-8 even their is i/p supply at terminals 23 & 24 and PFC display is showing power factor 0.3. So is PFC-8 is not in working condition, if no then what are the other check points.

Please suggest me

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Power Factor Controller L&T PFC-8

12/28/2011 10:08 AM

L&T has one of the best sales and service networks among Indian electrical companies. Are they not helping you? Have you asked them?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
3
Power-User
Engineering Fields - Electrical Engineering - Ron Nombri Engineering Fields - Energy Engineering - Ron Nombri Engineering Fields - Power Engineering - Eternal Power Papua New Guinea - Member - Ron Nombri

Join Date: May 2007
Location: Papua New Guinea
Posts: 174
Good Answers: 3
#2
In reply to #1

Re: Power Factor Controller L&T PFC-8

12/28/2011 10:31 PM

This is just a guide to assist with your problem on your PFC-9 Unit.

I've had similar problem and had relocated the C.T to the line side of the ATS (utility supple side), and reconfirm the C.T program settings at the controller. After which the unit was commissioned.

1. Do you a manual of the PFC-8 Unit?

2. Has an error massage appeared on the PFC-8 Unit's Controller?

If there is an error massage, check out the error at the "Trouble Shooting" page for remedy actions.

3. No voltage at o/p pins 1,2,3,4,5,6 indicates that the PFC-8 Unit controller is not switching their respective internal relay on.

PFC Unit controllers continuously monitors loading, and will switch on the internal relay of respective cap banks to energize the cap contactors engaging the cap banks into service. The number of cap banks coming into service depends on the loading magnitude, for power angle to be corrected to the set power factor. Cap banks are switched into service via a set electrical stepping sequence. Your controller will have a number of specific stepping sequences for 8 steps.

4. Check the C.Ts and the V.Ts if they are good, lose connection. Check if the meters are reading voltage, current, kw, and kva from your system loading. Check that jumper connections at the C.T terminal block is correct. Check that C.Ts are connected correctly in regards to polarity.

PFC Unit controllers depend on the C.Ts and V.Ts for loading data to determine the loading angle and the correction factor to maintain the set power factor, by which it engages cap banks via the o/p switches.

5. Check the PFC Unit controller settings, for all correct parameter settings.

a. Set power factor requirement is as required.

b. Correct Wiring configuration is set.

c. THD Limit

d. Electrical Stepping Sequence.

e. C.T ratio setting; controller will be unable to operate on excessive loading if C.T is oversized.

f. Metering Functions.

g. Thermal Control Setting, temperature limit.

Also as maintenance,

6. Check other hardware.

a. PFC Controller circuit breaker is good.

b. Terminal fuses between o/p terminals of controller and cap bank contactors coils, if there exists a fuse type terminal block.

c. Check contact coils.

d. Check cap bank fuses, remember to isolate unit.

__________________
Kind regards, Ron
Register to Reply Good Answer (Score 3)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: Power Factor Controller L&T PFC-8

12/29/2011 3:54 AM

Thanks very much, but i am not the one asking

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - Ron Nombri Engineering Fields - Energy Engineering - Ron Nombri Engineering Fields - Power Engineering - Eternal Power Papua New Guinea - Member - Ron Nombri

Join Date: May 2007
Location: Papua New Guinea
Posts: 174
Good Answers: 3
#6
In reply to #3

Re: Power Factor Controller L&T PFC-8

12/29/2011 5:31 AM

kvsridhar,

My sincere apologise, with due respect to your senior ship in the practice of Elect. Eng.; I had mistakenly replied to your post when I posted comments.

__________________
Kind regards, Ron
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7
In reply to #6

Re: Power Factor Controller L&T PFC-8

12/29/2011 7:32 AM

oh no! Not to worry! Please look at the goofy smiley at the end of my post...i was making a feeble joke! Please don't take it seriously. The main thing is that you gave a good answer, and everyone benefits...keep it up!

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #1

Re: Power Factor Controller L&T PFC-8

12/29/2011 4:40 AM

Thanks for the compliment, KVS! I am prouder to be an L & T'ite now.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Power Factor Controller L&T PFC-8

12/29/2011 4:41 AM

Why don't you talk to your nearest L & T Office?

Register to Reply
Participant

Join Date: Dec 2011
Posts: 1
#8

Re: Power Factor Controller L&T PFC-8

12/31/2011 11:50 PM

Hi,

You need to re-configure PFC-8. Some of the important checks before re-configuring the PFC-8.

1) Check CT input polarity and ratio of CT. CT rating must be more than your load current, If load current is more than CT rating than CT will saturate and PFC-8 will malfunction and same thing will happen if CT polarity is wrong.

For re-configuration, set below mentioned parameters

1) Setting of required PF

2) Setting of C/K ration

3) Configuration of capacitor bank

4) No of capacitor bank

5) Capacitor bank switching delay.

User manual will help you to re-configure PFC-8. If earlier it was in running than check above mentioned before re-configure check. You will definately get the result.

Register to Reply
Associate

Join Date: Jul 2011
Posts: 32
#9
In reply to #8

Re: Power Factor Controller L&T PFC-8

01/04/2012 12:17 AM

sir,

I check whole wiring diagrame & got ct sensing problem due to carbonised contact now PFC-8 is working in auto but display is blinking variable digits like 45 & 5 & indicating alarm too. I am using 5 set of capacitor in which one of them is not coming in activation at auto function so i am unable to know my correct pf value. Please help me what & where is the problem.

I don't have user manual & system was working earlier before these problems.

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #9

Re: Power Factor Controller L&T PFC-8

01/05/2012 7:29 AM

Get a replacement manual directly from the original equipment manufacturer.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Jul 2011
Posts: 32
#10
In reply to #8

Re: Power Factor Controller L&T PFC-8

01/04/2012 12:54 AM

sir,

Please discribe about C/K setting.

Register to Reply Off Topic (Score 5)
Register to Reply 11 comments