Hi Pot Testing Cable

12/29/2011 4:31 PM

will hi pot testing old direct buried cable cause damage?

Register to Reply
Pathfinder Tags: hi pot cable testing
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: utility contractor

12/29/2011 5:02 PM

It shouldn't if done properly. If you do damage them it's probably better to find out the weakness anyway. I have to ask though, are you really going to trust my word over somebody with authority at your utility?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: utility contractor

12/29/2011 5:09 PM

The purpose of the test is to find out whether or not the cable is damaged.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: utility contractor

12/29/2011 5:19 PM

I'd run it through the cable wash first and then be sure it's dry before testing.

(See previous posts too)

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#4

Re: utility contractor

12/30/2011 2:41 AM

It will reveal damage not cause damage.

Follow the instructions provided with your test set.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#5

Re: utility contractor

12/30/2011 7:31 AM

Yes and No, is the answer here!

The application of the cable has to be understood before deciding to HP it.

does HP testing damage cable? Yes it does, as does insulation testing or "Megger" testing (to those that don't know).

Several papers have been written.. and when I find them or the links I will include them, on testing cables, stating that HP testing WILL damage cable insulation .

As for the cable being dry, again two schools of thought here. In the oil industry for submersible cables, we HP them dry then wet in a water bath.

Over use of both insulation testers and HP tests will break down the insulation properties of the conductor insulation.

So in answer to your question, it can cause damage, however if the cable has never been HP tested before, then its unlikely. BUT I would "Meggar" test first, if the readings are low then you could try HP testing, but make sure you have the manufacturers data sheet BEFORE you start

AS I write all this, it has occurred to me that maybe you are unsure of the age of the cable and it's either never been tested or something has happened, maybe breakers have tripped??

whichever the case may be, then first I would use a 3000v or 5000v Insulation tester (Megger) the latest electronic ones are good, as they record the test values, if the cable fails that test, then its "dig it up time".. either replace or cut out the damaged section and use cable joints.

__________________
The square root of nothing is what you make it!
Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#6

Re: Hi Pot Testing Cable

01/01/2012 4:00 AM

I am wondering about such questions lately :) It could! I assume it would be shorter length power cables? High frequency....Apply the right voltage that's all...

__________________
--
Register to Reply
Register to Reply 6 comments