We have purchased ASCO make ATS of 4000 A , 440 VOLT. during meeting With technical person of ASCO , he told us about transfer of Neutral form DG to MSEDCL supply and vice versa takes very few time so as it dosent affect motor startes and other lighting. I have a question , can we connect DG neutral to MSEDCL supply while transfer takes place?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: May 2011
Posts: 84
Good Answers: 1
#1

Re: Neutral Transfer

12/31/2011 2:04 AM

Yes, but momentarily.

If utility and DG neutrals are connected both, then it may result in circulating current in the system through neutral during load unbalance.

Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#2
In reply to #1

Re: Neutral Transfer

12/31/2011 2:42 AM

I don't quite understand that.

Consider a Y secondary primary feed from a trasformer with neutral grounded.

Assume the DG neutral is connected to the same neutral and ground.

If the three power phases are open before the transfer, and there is a load imbalance, the neutral is still at ground potential at the point of common connection.

However, if the neutral point of common connection is "not common", then the neutral at the DG would float above ground potential, but there would be no circulating current unless the DG neutral was also grounded independently.

Register to Reply
Commentator

Join Date: May 2011
Posts: 84
Good Answers: 1
#3
In reply to #2

Re: Neutral Transfer

01/01/2012 9:41 AM

Dear GW,

Transfer from DG to utility supply involves synchronizing the two sources first and then opening the breaker of desired power supply.

If, DG is AMF (Auto on Mains Failure) type, then yes what you have explained is correct.

Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#4
In reply to #3

Re: Neutral Transfer

01/01/2012 11:53 AM

I understand that. Thanks.

My point of reference was a small 600V 75KW DG for a Fish Hatchery that auto starts on mains power failure (AMF). I did not switch the Neutral or the grounds, but did transfer (switch) all three phases. The OP had me doubting what I did, but the transfer switch came with just the three phases.

(We used to annually lose 1000's of fish on mains failure. One year it was 100% lost - approx 250,000 fish. Ten years ago we installed the DG and the loss due to power failure is now 0.)