Resistive Current Limiter

01/06/2012 8:23 AM

From all of the answers received relative to my previous question regarding limiting inrush current. I have decided to go with the resistive load and switch it out of the circuit using a parallel switch. Question: If my sourse is 240 vac and I want to limit the current to 4.8 amps, then I would use a 50 Ohm resistor as determined by R = V/I, but what power handling capacity would the resistor need to be? The largest ones that I can find are 100 Ohms, which seems to be well short of what should be required.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Resistive Current Limiter

01/06/2012 9:19 AM

Search high current resistors on Google

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: Resistive Current Limiter

01/06/2012 10:11 AM

i may be misreading your post...please check :

1. You want to limit the current to 4.8A so R = 240/4.8 = 50Ω

2. You want to know the power which is I²R = (4.8)² x 50 = 1152 W so, to be safe you need say 1.25 kW ... gosh, that is high !

So where does the 100Ω come in?

Since you say inrush, it may be a short-duration one, the wattage can be lower, depending on the duty cycle.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Commentator

Join Date: Oct 2010
Posts: 76
#3
In reply to #2

Re: Resistive Current Limiter

01/06/2012 10:26 AM

Hi,

The reference to the 100 Ohm resistor was an error on my behalf. It was meant to be 100 watts.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#4
In reply to #3

Re: Resistive Current Limiter

01/06/2012 10:40 AM

Ah...bad news then eh? 1.25kW would be massive. What is your duty? If it is 10s On, 30s Off, you may need only 100W (just a guess, don't hold me to it)

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#6
In reply to #4

Re: Resistive Current Limiter

01/06/2012 10:58 AM

Perhaps you mistyped 30sec, where as you were intended to say somewhere near 100 sec.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7
In reply to #6

Re: Resistive Current Limiter

01/06/2012 11:45 AM

Actually, i wasn't really meaning any real numbers....just giving the OP a feel of intermittent duty.

i have done some programming to calculate the intermittent ratings of resistors but that requires the time-constant for making any sense.(T = [Tm x e-(t/θ)])

Now, who would have that ? Very unlikely here, going by the posts so far.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#5
In reply to #3

Re: Resistive Current Limiter

01/06/2012 10:52 AM

You can use a 1 KwW Heating element used in domestic heater, or Buy a 50 Ohm 5 Amps Rheostat.

Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#8

Re: Resistive Current Limiter

01/06/2012 2:19 PM

There are many ways to do this. A safe way would be to parallel multiple power resistors to split the power dissipation between them. For example if you purchased these 130 watt, 1500 ohm resistors, and wired 30 of them in parallel, you would have a 50 ohm, 3900 watt load. A very adequate safety margin, albeit a $300.00 solution.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9

Re: Resistive Current Limiter

01/06/2012 3:24 PM

Are you still using this basic schematic? Did you set up the shorting contactor like I suggested back in October?

If so, the current limiting resistor need only be in the circuit between the 240V input and the top terminal of Variac #2, basically just to limit the inrush through the portion of winding used in Variac #1 because #2 will already be inherently limited as well. So do you want to limit that inrush to 4.8A then? And if so, how often is it going to be energized? Seems to me this is for a test bench application. Even a moderate wattage resistor may be able to handle that once a day or even once an hour. I also like the idea of using a heating element as a resistor. A "strip heater" is a good choice because it has a bigger surface area which means your watts desity will be lower and safer if someone touches it.

Didn't want to go with the NTC thermistor eh?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Commentator

Join Date: Oct 2010
Posts: 76
#10
In reply to #9

Re: Resistive Current Limiter

01/07/2012 4:31 AM

The heating element sounds a good bet; cheers. There would be no duty cycle as such. The device would be swithed on and left on for a time period anywhere between 30 seconds and 5 minutes, however, the off period would be totally random.

BTW the load (output) is a 20kV transformer.

Yes, the basic layout of the two variacs is as in the drawing. The parellel switch is installed in parallel with the 240 volts input; just need this resistor I am questioning about now. I didn't go with the NTC Thermistors because they obviously require a cooling down period to restore their higher resistance and thus their function.