Hi All,
In our site, we have a 200kV Switchyard. When we charged the switchyard and included the bus PT(220kV/110V), within 5 hours the R-phase PT was blasted with the top cover thrown away.
We replaced the failed PT with new one. Before installing the new PT, we completed the tan(delta) test for the PT. Earth Resistance of the PT base were checked and found OK. We charged the PT and found that after three hours the replaced PT also blasted. The line is unloaded. We have a wavetrap fpr PLCC system before the switchyard. Also we found that two more PTs after the Bus were also in the verge of failure.
The insulation class of the PT is 3P. Core Type two winding(secondary) transformer
1. We tested tan(delta) of all PTs and found satisfatory result.
2. We tested the earthing and found it was fine.
3. We checked the secondary resistance (loading) of the PTs and found that it is not crossing more than the PT burden (50 VA).
What could have caused the PT failures? Kindly suggest ways to resolve the issue.
Thanks in advance
N V M