Transformers

01/09/2012 4:04 AM

What is direct hot spot measurement in transformers?? Whether it is applicable for all transformers or any certain restrictions followed???

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
4
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: Transformers

01/09/2012 6:34 AM

Transformer manufacturers do a heat-run test on their transformers and they know the hottest spot in the winding during a rated load condition. It is better to install your temperature sensing device in the hottest spot to provide a good degree of thermal protection to the transformeer. It is applicable to all Power Transformers and to all Distribution transformers. Both to the Oil type as well as the Dry type.