Current Transformers

01/09/2012 3:18 AM

I want to replace some CTs in a switchgear and i just observed that the existing CTs have an extra terminal with a capacitor symbol on the terminal and the new one to be used does not have that same terminal, meaning that particular connection can not be made. Unfortunately, The existing and current drawing does not contain this connection.

Each CT block has within it, two transformers( protection and metering)

Protection CI.5P15/10VA, 100/1A

Metering: CI.1/15VA, 100/5A

In total 3 blocks for the three phases; with one protection and one metering contained in each block. The switchboard is a 20 KV ABB switchgear.

NB

I really dont know the importance of this connection as it applies presently to the switchboard.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Participant

Join Date: Jan 2012
Posts: 3
#1

Spam

01/09/2012 3:42 AM

CR4 ADMIN: Deleted Post

Spam: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

Register to Reply Off Topic (Score 4)
3
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Current Transformers

01/09/2012 6:43 AM

The extra terminal with a capacitor symbol in the existing CTs could be the potential equaliser terminal. This terminal is normally connected solidly (with a 2.5 sq.mm insulated Copper wire) to the respective phase bus bar on which the CT is installed. This is to equalise the potential between the inner wall and the outer wall of the CT insulation. If not done, the potential difference existing between the inner wall of the CT (which could be at the phase voltage of the installtion) and the outer wall of the CT (which could be at earth potential) - can builkd up capacitive charges thro the CT insulator material and thus the CT insulator material gets stressed, leading to its pre-mature failure. This is normally practice in all MV Indoor Board mounted CTs.

I don't understand why the new CT in your case does not have this potentiual equaliser terminal. It is a good practice to provide this terminal on to board mountable MV CTs. May be the new CT has a better insulation to tolerate any such stress. Or, may be you sourced your CT from a not-so reputed manufacturer. Pl. speak to the CT vendor and set it right. If I were you, I would insist on the provision of a potential equaliser terminal on the CT.

More importantly, the terminal has to be connected to the bus bar. But, don't take my word - as I am only guessing. Talk to your peers.

Register to Reply Good Answer (Score 3)
Commentator

Join Date: Nov 2009
Posts: 89
#3
In reply to #2

Re: Current Transformers

01/10/2012 7:21 AM

Thank you Very Very Very Very!!!!!!! much. I appreciate your prompt response. In my MV board the terminal is connected to the respective phase bus bar on the CT installed to some phase line indication lights in front of the panel. My main question: How is the potential equalization realized, because of the connection on the CT capacitor terminal.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #3

Re: Current Transformers

01/11/2012 7:31 AM

The terminal on the CT with capacitor symbol marking may probably be tapped from the outer wall of the CT's insulated enclosure. This outer end of the CT enclosure (and thus the terminal marked with the capacitor symbol) forms one plate of a capacitor. The inner wall of the CT which is in proximity to the live bus bar forms the other plate of a capacitor. There is a solid dielectric (may be epoxy resin) between these two plates. This construction of two plates seperated by a dielectric is called a capacitor. Isn't it? Now, when to short the outer terminal on the CT to the bus bar of the phase on which this CT is mounted, you are literally shorting the two plates of this capacitor (i.e.) the potential between the inner and the outer walls of the CT will be same. There will not eb any potential differenec and hence no capacitive leakage currents thro the CT insulation, thus saving the insulation deterioration.

And, the indication lights installed in the front of the panel are called "Live Line Indicators". They work on the principle of Capacitor Potential Divide. You take an insulator. One end of the insulator is at the bus voltage and the other end of the insulator is at ground potential (thro the mounting bolt). The insulator is a dielectric. Now, the two ends (the bus end and the panel end) of this insulator form plates of a acpacitor and the insulating medium of the insulator is the dielectrc, thus forming a capacitor. Even though you would see a solid insulator, it, in fact, is made up of discreet smaller cell capacitances. Now, if I tap a wire from the centre of the insulator, I can mesaure approximately half the phase voltage of the bus bar which is mounted on to this insulator. As the tapping point is nearer to the bus you would get more voltage and as you tap nearer to the panel end, you would get less voltage. Now, if can locate a point on the surface of the insultor, where if I tap, I can get, say, 110V, can I not use this to power an indication lamp? And, as the voltage on the bus bar varies, the tapped voltage also varies very linearly, thus indirectly performing the function of a Potential Transformer. The only problem in such an arrangement is that this capacitor potential divide cannot drive a large current thro the burden. SO, ot may work for smaller burdens like an LED lamp. In one of my previous employments, I have developed a digital voltmeter, which would work on signals from this capacitive potential divider. Such an arrangement, we used to call, "Voltage Sensors".

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Nov 2009
Posts: 89
#5
In reply to #4

Re: Current Transformers

01/12/2012 8:23 AM

Thank you very much. Your immense contribution to this matter cannot be over stated. Thank you very much.

We just wrote to ABB to provide us with a logical explanation why they have made such changes. Presently, nothing has been said yet. Thank you very much and have a wonderful afternoon.

Register to Reply
Commentator

Join Date: Nov 2009
Posts: 89
#6
In reply to #4

Re: Current Transformers

01/19/2012 8:04 AM

Good afternoon,

Please i am in search of professional certifiactions i need to better position myself as an elctrical and instrumentation engineer. I have been involved in the contruction and installation of gas turbine power station and presently i am involved in the revamping of an oil and gas flow station(electrical). I have been searching the internet for professional certifications i can obatin that will enable me work as a professional, internationally. Please can u help me with any information. Thank you in anticipation.

Presently, i only have a university degree in electrical electronics engineering.

Regards,

ifidon

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#7
In reply to #6

Re: Current Transformers

01/21/2012 3:59 AM

Find out what types of certifications are required for the positions you are interested in and start accumulating.

There must be some job ads you were interested in. What did they ask for?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

benotype (3); brookdai (1); electricalexpert65 (2); Wal (1)

Previous in Forum: Comments on Short Circuit Calculation Needed   Next in Forum: Transformers

Advertisement