Comments on Short Circuit Calculation Needed

01/08/2012 11:37 PM

Hello everyone. I am new college pass out. I got some electrical drawing and calculated the short circuit but there is variation between my calculation and the contractor calculation. Here I have attached my calculation please comment on it (Not a home work question). I want to know any other factor to be included in the calculations. I made my calculation as per IEC 60909.

22kv Line ,z=1.29,Cmax=1.10 and Cmin=1.0

MAXIMUM SHORT CIRCUIT CURRENT

INITIAL SYMMETRICAL SHORT-CIRCUIT CURRENT =Cmax * 22000/(1.732 * 1.29)

=1.10*22000/2.23

=24200/2.23

=24200/2.23

Ik" = 10852.01A ~ 11KA

PEAK SHORT CIRCUIT CURRENT (Ip) =K * 1.414 * 10852.01 (value of k obtained from graph)

=1.6 * 1.414 *10852.01

= 24551.58 A

MAXIMUM SHORT CIRCUIT AVAILABLE AT 22 KV = 24551.58 A ~25KA

MINIMUM SHORT CIRCUIT CURRENT

INITIAL SYMMETRICAL SHORT-CIRCUIT CURRENT =Cmin * 22000/(1.732 * 1.29)

=1*22000/2.23

=22000/2.23

Ik" = 9865.47A~ 10KA

Should i calculate the first peak of the fault current for minimum fault current (Ip) or go a head with the initial symmetrical fault current Ik" (ie minimum Fault current =10KA)

PEAK SHORT CIRCUIT CURRENT (Ip) =K * 1.414 * 9865.47 (value of k obtained from graph)

=1.6 * 1.414 *9865.47

= 22319.63 A~23 KA

MINIMUM SHORT CIRCUIT AVAILABLE AT 22 KV= 22319.63 A ~23 KA

Register to Reply
Pathfinder Tags: Short circuit calculation.
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Comments on Short circuit calculation needed.

01/09/2012 12:20 AM

Well it's nothin to be ashamed of, I passed out a few times during my college years....Now what are all these calculations about, transformer, generator, something new?

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Associate

Join Date: Sep 2011
Posts: 47
Good Answers: 2
#2
In reply to #1

Re: Comments on Short circuit calculation needed.

01/09/2012 1:18 AM

Its about a generator connected to 11 Kv line to export power to 22Kv line tranformer data :12 MVA,z%=8

Register to Reply
Participant

Join Date: Jan 2012
Posts: 3
#3

Spam

01/09/2012 3:44 AM

CR4 ADMIN: Deleted Post

Spam: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Comments on Short circuit calculation needed.

01/09/2012 6:47 AM

You have not considered the source impedance and the transformer impeadnce. You ahve only included the line impeadnce. That's why you get the variation. Pl. read IEC 60909 more carefully. It definitely takes intgo account the source impedance and the transformer impedance.

Register to Reply
Associate

Join Date: Sep 2011
Posts: 47
Good Answers: 2
#7
In reply to #4

Re: Comments on Short circuit calculation needed.

01/09/2012 9:04 PM

Thanks for your reply...and for minimum short circuit current should i calculate the first peak value of the current (Ipmin)?

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8
In reply to #7

Re: Comments on Short circuit calculation needed.

01/11/2012 7:37 AM

Any short circuit calculation involves calculation of two values, the symmetrical RMS values of the short circuit current (to arrive at the required short circuit breaking capacity of the Short Circuit Protective Devices and to calculate the thermal effects of the short circuit current) and the first cycle Aymmetrical Peak value of the short circuit current (to arrive at the required short circuit making capacity of the circuit switching devices as well as to calculate the electrodynamic stresses developed during the short circuit).

These values (RMS & Peak) have to be calculated both for the minimum short circuit current as well as the maximum short circuit current. The minimum and maximum values of short circuit current mentioned in the Standards are pertaing to certain assumptions that may prevail during the short circuit.

Register to Reply
Member

Join Date: Jan 2012
Posts: 5
#5

Re: Comments on Short circuit calculation needed.

01/09/2012 8:15 AM

Dear friend,

please teach me. i am also intrest in short circuit calculation. what is the graph for K value, what is the 1.414 value. please replay me. or send by mail. PEAK SHORT CIRCUIT CURRENT (Ip) =K * 1.414 * 10852.01 (value of k obtained from graph)

Regesh kumar.

CR4 Admin - email address removed

From the CR4 Rules: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers and email addresses posted in threads or comments. You can share this information via the CR4 internal messaging system.

__________________
Regesh kumar
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #5

Re: Comments on Short circuit calculation needed.

01/09/2012 12:21 PM

Please do not expect us to provide you with a free education. Do some basic research ON YOUR OWN!!!!!!!!!!!!!!!!!!!!

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#9

Re: Comments on Short Circuit Calculation Needed

10/06/2012 2:16 PM

Please try this link

__________________
Ramesh,Freelance Electrical/automation Consultant