Transformer With Two Tap
01/10/2012 3:58 AM
Hi all!
I have a transformer with two tap and I am having a hard time finding the right setting. I used to transformer with just one TAP. What the second for?!? It is 630KVA, 15000KV/400 volts, 50Hz. The transforme rhas two taps:
TAP 1 2
1) 15500 20500
2) 15000 20000
3) 14500 19500
I bought the transforme from France, it is a Merlin Gerin transformer , oil filled. It was set from the factory to 2. When did connect it to grid ,the secondary was giving me between phases 302 V instead of 400 volts as it was supposed. And 175 v phase and neutral. What should I do in order to have 400 Volts on the secondary? Should I move the both TAP to position 3?
Please help, Page
Good Answers: 181
Re: Transformer With Two Tap
01/10/2012 8:57 AM
If you move the tap settings you're only going to gain 10V or so.
What is your supply voltage?
01/10/2012 9:05 AM
The supply voltage is 15000v. Why we have two taps in the first place?
01/10/2012 9:33 AM
Where's the paperwork that came with the transformer?
01/10/2012 12:20 PM
Dear Lyn,
The paper work does not say much! Why do we have two taps? This is the first I am seeing a transformer with two taps. Best Regards, Page
01/10/2012 12:34 PM
Your supplier should idientify the values of each tap. Are you new to the business?
Call your supplier and explain that you don't know how to hook the transformer up properly.
Tap (transformer) - Wikipedia, the free encyclopedia
01/11/2012 12:23 PM
Thanks Lyn, I will contact the supplier regarding the 2 taps. Page
01/11/2012 12:23 PM
Dear Mr.Page
It appears the transfprmer is duel voltage transformer viz 15 KV/400 V and
20KV/ 400 V nominal.For your supply system of 15 KV please select tap 1 and you will get 400 Volts on the secondary (nominal) (300/15x20=400 ).You can adjust the tap 1 to position 15 KV or 15.5 KV or 14.5 KV as per your available system voltage to get almost 400 V on the secondary.
You are now getting 300 V as you are applying 15KV in 20 KV tap
01/11/2012 1:11 PM
Ok Ramasmi, if you are right then how do I know where the incoming voltage(15KV) is applyied to? To tap 1 (15,5kv, 15kv, and 14,5kv ) or tap 2 ( 20,5kv, 20kv, and 19,5kv)?Since both taps (1 and 2) are sitting on the top of the transformer and set originally from the factory to position 2( tap1 15kv, tap2 20kv)! Each tap has position 1,2 and 3. There is no such thing as transfer switch to switch the incoming voltage from tap 2 to tap 1 and apply what you are suggesting. Is the incoming voltage applyied to both taps(1 and 2)?How is the wiring inside this transformer in relation to both taps? I will keep trying to contact the suppliers( I am in Africa and I did not buy this transformer myself) as suggested by Lyn.
Thanks, Page
01/12/2012 9:34 AM
Dear Mr.page
You have to connect to tap 1 position 2 which is meant for 15 KV and measure the secondary voltage.If it is 400 volt leave it.If it is less connect to position 1 which is meant for 14500 V and if it is more connect to position 3 which is meant for 15500 V.
Better you check what is the incoming voltage at your supply point and connect accordingly
Normally manufacturer provides selector switch to choose the position 1,2,or 3.Please check with manufacturer
01/14/2012 12:06 AM
I moved the tap from position 2 to 3, 14,5kv, almost the same result. I think the transformer was made to receive 20kv as incoming voltage. I am pretty much sure that the manufacturer made just a mistake and shipped the wrong transformer. When we received the transformer the name plate was not attached to it. I am still wondering why do they make transformers with two taps?
01/14/2012 1:18 AM
you din't mention if you have connected to tap 1 instead of pre connected tap2.Unless you connect to tap 1 you wont get the required voltage of 400V nominal
01/14/2012 6:35 AM
Look Ramasmy, We have two Taps, TAP 1 and TAP 2 and each one has 3 positions, 1,2 and 3. Originally from factory (I guess) both taps were set to position 2. What we did yesteday was move TAP 1 from position 2 (15KV) to posotion 3 (14,5KV). Still we could not get the 400V on the secondary! The manufactures have not got back to me yet. Why two TAPs? Anybody knows?
01/14/2012 7:02 AM
Dear Mr.Page
As i mentioned earlier until and unless you connect your incoming supply to TAP 1 instead of existing Tap 2 you wont get 400 V out put irrespective of position 1,2,or 3
Regarding two TAPs, it is to fecilitate to suit different power supply in different countries whre 20 KV is also standard as 15 KV is staandard in your coun try
01/16/2012 1:43 AM
Dear Ramasmy: How do I connect the incoming supply on TAP1 ? !?!?Are you familiar with big power transformer?
What do you mean by ´Regarding two TAPs, it is to facilitate to suit different power supply in different countries where 20 KV is also standard as 15 LV is standard in your contry´?
Page
Good Answers: 102
01/12/2012 12:07 AM
While waiting for the manufacturer to guide you, perform some experimentation.
Deciding on which tap to use is really dependant on knowing the turns ratio of the trafo.
You can energise the primary side with LV and measure the secondary voltages presented at each tap. This will give you further insite but you should still chat with the supplier as they should know (unless it is 60 years old, or emblazoned with Chinese text, or something like that)