i have facing problem in eurotherm made DC drive 590 series
today morning our operator complaint me that machine is not starting,then i checked and found 2 no's of 80A fuse at the i/p of drive are damaged so i replaced 2 with the same capacity fuse.then when we started again all 3 fuses r damaged with some sparking sound.then i checked the drive and found that drive i/p is directly shorted with each other.i opened the drive and found that 2 no's of thyristors r damaged.means fully bursted. it is 4Q driive with 460vdc armature volt with 70 amps.i tested the motor and it was found okk.also we started motor slowly not kept in high speed.so pls give ur ideas what prob may caused 2 scr to damage?also can i connect 2 fuses to o/p of drive? i mean with A+ and A- so that if there is any prob with motor so that these fuses should blow first before damaging drive.if yes what type of fuses should recommanded ? pls give me specification for 70A so that i can purchase.
thanking you
Re: DC Drive Prob
01/10/2012 11:09 AM
I'm not trying to be be mean but I think this stuff is over your head. You're dealing with some strong stuff, you can't guess your way through it. When I was in electricity school I had an instructor that used to say "you'll forget, electricity will never forget and it will remind you when you do". I suggest you get a factory trained technician to come out and make factory repairs before someone gets hurt.
Re: DC Drive Prob
01/10/2012 2:00 PM
It seems that SCRs have completed their useful life.
you can replace damage SCRs and test drive in solo that without connecting motor.
Motor can be tested seperately.
Good Answers: 804
Re: DC Drive Prob
01/10/2012 2:06 PM
What casued the final dmage to the thyristors is that you replaced the fuses without first determining WHAT casued them to blow in the fist place. You performed what is jokingly called a "smoke test" on a very expensive piece of equipment. In all likelihood the original problem may have involved one bad thyristor or something less damaging like a bad firing board, but you compounded the problem by pumping short circuit current into the drive and now you will never know. Most likely it is now also damaged beyoud repair, you had better budget for a new drive.
Fuses on the oputput are pointless. The drive will have output short circuit protection for the motor that will be faster than the fuses anyway. It's highly unlikely that a modern digital drive can be damaged by anything in the load side that fuses would protect against anyway. If something bad did happen, by the time the fuses cleared the drive power electronics is long gone.
As previously suggested, you need an experienced professional to take care of this for you.
Re: DC Drive Prob
01/10/2012 2:20 PM
JRaef as you said may be its prob with 1 thyristor, because previously also this drive was tripping with over current fault without load,when machine was suddenly stopped.
i think that it was problem with regenerative thyristor or with that circuit.now there is totally 2 thyristors r damaged. but pls let me know is it possible to test firing circuit with multimeter? if yes how can i do? because i am in Kuwait (arab country) where we cant find any good dealers and technicians to do all this jobs.so we only do all this things in our company.also we cant find spare parts also for many things here.
Re: DC Drive Prob
01/10/2012 3:04 PM
Take several detailed pictures...with close-ups of the controls. Maybe we can save you a little time.
Good Answers: 38
Re: DC Drive Prob
01/10/2012 11:10 PM
are you a certified maintanence engineer?
Good Answers: 42
Re: DC Drive Prob
01/10/2012 11:57 PM
The PIV of SCR's do degrade with time and use.
You state this is a 4 quadrant drive - therefore you may have had an inverting fault. That can be a drive failure, cross fire, low mains voltage, poor cml loop tuning, even a bad tachometer can cause havoc.
Rockwell, and ABB both protect their 4 quadrant bridges with fuses an the mains and on the DC side if it uses only three line fuses. If the drive uses 6 leg fuses then the DC side fuses are not used.
If you are not comfortable with commissioning this equipment (from the ground up), then get a qualified service tech.
Re: DC Drive Prob
01/11/2012 8:23 AM
at Epke yes i am certified maintenance engineer,but i am looking all plant maintenance including mechanical works so i didnt went fully inside the drive maintenance.
and GW. this design is working well from 15 years.this is 15 yrs old machine.as u said i also feel that its prob with regenerative circuit.so now i am purchasing the thyristor module and will see the result.but again here in original design they only used 3 fuses at the drive i/p which is 80amps.so now i want to place 2 fuses at the drive o/p. but what type of fuse will act fast and clear fault? and what i am thinking is right or wrong? if right what type fuse u recommand?
Good Answers: 42
Re: DC Drive Prob
01/11/2012 11:05 AM
ABB uses the same size and type as the three line fuses which are semiconductor current limitting fuses. Rockwell tends to use fuses about 1.25 times larger on the DC side, but again semiconductor type fuses similar to the ones used on the AC side. These fuses must have a DC interupting rating.
Reliance electric often used molded case circuit breakers on the dc side with the three poles in series to get the DC interupting capacity. Magnetic trip only, with trip setting about 200% to 250% of motor full load amps. Again, the CB must have a DC rated interrupting rating. The DC rated interrupting capacity will be much lower than the AC rating.
Good Answers: 102
Re: DC Drive Prob
01/11/2012 11:34 PM
That would be 3 poles in parallel to get the higher interrupt capacity. Right?
Good Answers: 42
Re: DC Drive Prob
01/12/2012 12:02 AM
No, in series! To get a higher DC voltage interupting. Your typical MCB will only have 250VDC rating. Put the 3 poles in series lengthens the arc better. MCB has to be rated for the full load amps x 1.25
Good Answers: 102
Re: DC Drive Prob
01/12/2012 12:28 AM
Roger that.
Ratings and capacities jumbled here. In my head at least.
I hear what you're saying.
Good Answers: 42
Re: DC Drive Prob
01/12/2012 1:13 AM
Hope this helps. This was for a 540HP 500V armature. 300/1200 RPM field range.
Good Answers: 19
Re: DC Drive Prob
01/11/2012 12:10 AM
Well, sometimes it is a good idea to read the manual.
Good Answers: 102
Re: DC Drive Prob
01/11/2012 8:42 AM
Have you considered using a circuit breaker between the drive and motor instead of the fuses you suggested?
You can compare the interupt time of different fuses and CBs with a bit of research on the internet.
Reason for SCR damage? They do fail and the failure of one can lead to a cascaded fault of the others. Are the SCRs correctly attached to their heatsinks? Is there adequate cooling of the heatsinks?
First failure in 15 years is a pretty good service history. What has changed?
If you have an Oscilloscope you can check this thoroughly.
Re: DC Drive Prob
01/11/2012 11:10 AM
JRaef is right you need a new Drive. (and the Service Manual with it)
It's not Rocket Science
Good Answers: 42
Re: DC Drive Prob
01/11/2012 3:35 PM
The nice thing about DC drives is they tend to be very reparable.
With the 590 drive there may be some MOV's on the main board. My experience has been when fuses blow the MOV's also explode damaging the printed circuit board. If the PC board is damaged you are out of luck. If the SCR's shorted then replacing them and the fuses (not a big job) will get you up and running.
The MOV's are round discs about 3/4 to 1 inch in diameter about 3 mm thick with 2 leads. When they blow the tend to rupture out the side and spew ionized gas around causing colateral damage. Again, not an expensive part by itself.