01/11/2012 4:25 AM

If there are 6.6 KV motor loads being fed from 6.6 KV Breaker panels and also LT loads are fed from 6.6 KV breaker panels through 6.6/0.433 KV Distribution transformer then should I go for 6.6KV APFCR panel or LT APFCR?

__________________
peace.
Register to Reply
Pathfinder Tags: HT APFCR
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: APFCR

01/11/2012 5:20 AM

Both.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: APFCR

01/11/2012 7:02 AM

6.6kV APFCR for 6.6kV Loads & LT APFCR for LT loads - if you want to gain maximum advantage of Power Factor improvement.