Shaft voltage

01/12/2012 1:15 AM

Are shaft voltages AC or DC or both in nature.?How much shaft voltage is a threat to the motor bearings?Is there any standard anybody knows?

Sincere thanks in advance.

__________________
"Know something about everything and everything about something"
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Shaft voltage

01/12/2012 3:24 AM

A voltage on a motor shaft is a symptom of insulation breakdown.

Why didn't the installation earth trip operate (rhetorical question)?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2008
Location: Van Nuys, CA
Posts: 563
Good Answers: 33
#3
In reply to #1

Re: Shaft voltage

01/12/2012 4:05 PM

"A voltage on a motor shaft is a symptom of insulation breakdown."

Not necessarily. I remember reading about this a couple of years ago.

A quick Google... appears to a fairly common problem with variable-frequency drives (VFD). The basic fix is a "shaft grounding brush/ring". Low-impedance shielded cables are also recommended.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Shaft voltage

01/12/2012 7:12 AM

I remember having read some good papers on the subject in the ABB Website. Pl. search in the ABB Website for Shaft Voltages/Shaft Currents.

Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Shaft voltage

01/12/2012 7:09 PM

It's AC, high frequency and it is the result of the high speed switching pulses in VFDs. It builds up in the rotor and looks for a path to ground through the bushings / bearings, causing the equivalent of EDM, which scores and eventually destroys the bearings and races. Grounding bushings provide an easier and safe path to ground.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#7
In reply to #4

Re: Shaft voltage

01/18/2012 9:39 AM

What will be nature of shaft voltage if there is no VFD used.?

__________________
"Know something about everything and everything about something"
Register to Reply
Guru

Join Date: Feb 2008
Location: Van Nuys, CA
Posts: 563
Good Answers: 33
#8
In reply to #7

Re: Shaft voltage

01/19/2012 12:44 PM

"What will be nature of shaft voltage if there is no VFD used.?"

Answered in posts #5 and #6, above.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: Shaft voltage

01/14/2012 10:51 AM

It can also occur with large wound rotor motors. Normally one bearing is mounted on insulators to stop circulating currents.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Commentator
Engineering Fields - Power Engineering - Siswanto

Join Date: Mar 2008
Location: JAKARTA. INDONESIA
Posts: 73
Good Answers: 15
#6

Re: Shaft voltage

01/15/2012 1:09 PM

SHAFT VOLTAGE

The shaft of a rotating machine ideally should have no voltage end-to-end or shaft to ground. However, such voltages do exist on almost all shafts due either to electrostatic charge build up or residual magnetism and, in electrical machines, to asymmetry in magnetic fields of the stator and/or rotor. Electrostatic charge build-up can come from charge separation in connection with steam or oil flow. Residual magnetism is often left in the unit from such causes as welding, magnetic particle inspection, plus permanent magnets or electromagnets possibly employed for holding, transport, etc. Magnetic asymmetries in the stator and/or rotor of electrical machines come from causes such as air gap eccentricity, shorted core laminations, broken rotor bars, winding shorted turns and/or ground faults, plus transients and harmonics from variable frequency or PWM power supplies or from blown diodes or fuses in excitation systems. So long as the shaft peak voltage to ground does not exceed 1 Volt, there should be no consequential effects to the bearings. When the peak shaft voltage exceeds 1 volt, there is a possible risk that current discharge will occur across that bearing, depending upon the magnitude and frequency of the voltage, the bearing loading, its alignment, shaft vibration and the condition and cleanliness of the oil film. The effect of the shaft voltage on bearings is electrical spark erosion, spark tracking or welding at shaft journals and bearing babbitted surfaces

IEEE Std 11 5-1 995

PART I-ACCEPTANCE AND PERFORMANCE TESTING

3.6 Shaft current and bearing insulation

3.6.1 General

Irregularities in the magnetic circuit may cause a small amount of flux to link the shaft, with the result that an electromotive force is generated between the shaft ends. This electromotive force may cause a current to flow through the shaft, bearings, bearing supports, and machine framework, and back to the other end of the shaft, unless the circuit is interrupted by insulation.

NOTE-

While other causes may produce a shaft voltage not involving a difference in potential from one end of the shaft to the other, special tests are not provided for the resulting effects because each of these sources requires specially adapted methods of test, essentially of an investigative research nature.

3.6.2 Method 1. Across end shafts

The presence of shaft voltage may be determined by measuring the voltage from end to end of the shaft with a high-impedance voltmeter.

3.6.3 Method 2. Across bearing oil film, uninsulated bearings

This method requires that the insulating properties of the bearing oil film be adequate to withstand the shaft voltage without breaking down. The presence of shaft voltage or current may be determined by running the machine at rated speed and voltage, and connecting a low-resistance conductor from the shaft to the frame of the machine at one bearing, and a low-range ac voltmeter (or a high-range ac ammeter) with low-resistance leads from the shaft to the frame at another bearing. Deflection of the instrument indicates the presence of a voltage that may produce shaft currents. If the instrument does not deflect, there is either insufficient voltage present or the bearing oil film is not acting as an adequate insulator.

3.6.4 Method 3. Across bearing insulation

Many machines have one or more bearings insulated to eliminate shaft currents. For these methodls as described in this subclause as well as 3.6.5 through 3.6.7, it is assumed that insulation is located between the bearing and the frame of the machine. To determine the presence of a voltage that will produce shaf,t currents in such a machine, a low-resistance conductor is connected from the shaft to the uninsulated bearing in order to short-circuit the oil film, and a low-range ac voltmeter (or a high-range ac ammeter) is connected between the shaft and the frame successively at each insulated bearing. Deflection of the instrument indicates the presence of a voltage that will produce shaft currents if the bearing insulaticln is not present.

3.6.5 Method 4. Bearing insulation

The insulation can be tested by connecting a low range altern,ating-current voltmeter (or a high range alternating-current ammeter) across the insulation. A low-resistance conductor may be applied from the shaft to each bearing to short-circuit the oil film. Deflection of the instrument, in this case, is evidence that the insulation is at least partially effective. If there is no deflection of the ,instrument, either the insulation is defective or there is no shaft voltage present.

3.6.6 Method 5. Bearing insulation

A layer of heavy paper is placed around the shaft to insulate the journal of the uninsulated bearings. The coupling of the driving or driven unit should be disengaged if it is not insulated. Then from a 110V - 125V scale with a resistance in the range of 100 Ω/V - 300Ω/V placedin series with the voltage source, two leads should be run, one of the insulated bearing and the other to the frame (across the insulation), if the lamp filament does not glow (or if the reading of the voltmeter does not exceed 60V) the insulation may be considered satisfactory.

A 500 V megger may also be used. This is much more sensitive than the above method and may tend to reject insulation which is adequate to prevent the small shaft voltage from causing injurious current.

Fig Ref, Bearing Damaged and Insulation

__________________
LOVE FORUM AND DISCUSSION
Register to Reply Score 1 for Good Answer
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: