Condensation Problem in Motor

01/15/2012 8:12 AM

we have 11kv induction cage motors of 400kw power with no space heaters installed.the motors are located in place where pipes and tanks of cool water are located.frequent condensation in the motors occur when motors are stopped for even one hour.the insulation resistance drops below 1mega ohm and we cannot then run the motor .we continously dry the motor using hot air blowers for many hours which is very tedious job and time consuming.

i want to know is there any other method of drying the motor which is less time consuming.we have no baking facility and the motors are too heavy to carried to a place where sun light will dry them.

i have read in some place that passing direct current for some time through motors will dry the insulation.now the problem is what should be the magnitude of DC voltage and dc current that should be passed through winding of the motor for drying it .assuming motor winding resistance per phase to be 2ohm and motor be the three phase induction cage motor of 11kv.

Looking for kind replies please.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Aug 2010
Location: VA
Posts: 84
Good Answers: 4
#1

Re: condensation problem in motor

01/15/2012 8:50 AM

Power would be E times I per winding, and you should be able to do some experimenting to determine the heat needed to overcome the rooms cooling. Id start with something like 10 amps and measure the resulting heating to see if it offsets the chilling. It sounds like your humidity in that room may be another problem to address, possibly more ventilation is needed. Woody

__________________
Life is short, eat your dessert first .......In theory there is no difference between theory and practice. In practice there is. Yogi Berra
Register to Reply
Active Contributor

Join Date: Aug 2010
Posts: 10
Good Answers: 3
#2

Re: condensation problem in motor

01/15/2012 10:22 AM

Another option would be using infra red lamps about the motor, connected through a spare auxilliary n/c contact of the staring device. It eliminates the need for dc power. And of course, as waldig suggested, better ventilation.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: condensation problem in motor

01/15/2012 10:50 AM

Why not install dehumidifiers to lower the moisture level prior to, and during shutdown? This would at least make the drying process faster...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#4

Re: condensation problem in motor

01/15/2012 11:16 AM

One of the things I have seen done to achieve what it is you need to achieve is the placing of rod or strip heaters against the outside of the stator. Heat is heat... whether generated on the outside that radiates into the case or from the inside, both methods should work.

As a benefit, by this method, you do not make any electrical connections to the windings and... control of the heater elements at the lower voltage is much easier.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: condensation problem in motor

01/15/2012 11:40 AM

Its a simple task at LV but not at 11kV.

There are pre-made Motor Winding Heaters that automatically apply the DC current to one winding. The problem is, it needs to be current controlled and very low voltage. Not a big deal on low voltage motors, but for medium voltage motors the equipment providing the low voltage DC must be completely isolated from the MV power when the motor is running. The necessary 11kV switchgear it will take to provide that isolation will be very expensive. If you build your own, you must also construct a way of measuring any residual voltage in the motor and know for absolute sure that the motor has stopped spinning before energizing the DC heater circuit, otherwise you will regenerate back into the DC supply unit and destroy it.

It will cost much less to fabricate some sort of external resistance or radiant heater for the motor that can be powered separately by LV. They make heater blankets and band heaters for things like this, I suggest you look into those.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru
Hobbies - DIY Welding - New Member

Join Date: Apr 2008
Location: Bristol, Tennessee
Posts: 1177
Good Answers: 58
#6

Re: condensation problem in motor

01/15/2012 11:47 AM

A dehumidifier may be the answer. Have one where all the heat from it is dry, direct that into the motor's cooling intake. Drain the condensate away from the motor room.

Some air conditioners use condensate to cool the condenser coils, eject a moist heat. You don't want that type. Split-types separate the two functions, all the water can be drained away, and all the heat goes to heat the motor.

__________________
mike k
Register to Reply
Commentator
Engineering Fields - Power Engineering - Siswanto

Join Date: Mar 2008
Location: JAKARTA. INDONESIA
Posts: 73
Good Answers: 15
#7

Re: condensation problem in motor

01/15/2012 1:41 PM

WINDING DRY OUT USING HIGH CURRENT SUPPLY

To dry out of stator winding for Large Motor or generator and Wound Rotor, High current with low voltage injection to the winding is the best solution when baking oven is not available or not possible to keep inside due to limitation the baking oven dimension.

Supply the winding by dc current in approximately 60 - 70 % from FLA and keep the temperature round +/- (max) 80 to 90 degrees Celsius for at least 12-16 hours, depend on the winding insulation capacitance and condition "how much winding wet due to moist absorption"

Connect the winding in 1 phase, when the winding is 3 phases with 3 lead cable (wye or delta connection), connect the 2 phases in one (let say Phase U & V, to be connect together), and connect the current supply to phase W to U-V.

To avoid imbalance heat distribution in the winding due to imbalance Resistance between phase W and phase U-V, change the connection between phases, ie:

1st dry out, phase W to U-V

2nd dry out, phase V to U-W

3rd dry out, phase U to V-W

If stator lead are 6 cables, connect the 3 phases (U,V,W) in one phase, and power supply to be connected to phase to neutral (x,y,z)

__________________
LOVE FORUM AND DISCUSSION
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Apr 2008
Location: Bristol, Tennessee
Posts: 1177
Good Answers: 58
#8

Re: condensation problem in motor

01/15/2012 1:50 PM

OP says the motors are only off for a few hours, then presumably they want to use them again. Hooking up a bunch of DC wiring between runs may be troublesome.

A: Shoot the engineer that located the motors in such a place.

B: Build a vapor tight enclosure for the motors, with humidity control. A tight structure should not cost that much.

__________________
mike k
Register to Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#9

Re: condensation problem in motor

01/15/2012 2:13 PM

I think that for some reason, water trapped inside motor body, cycles between phases. What I can not understand is why you don't heat it and at the same time give water a path to get out (possibly help it by vacuum or silica) and then seal all the possible ways it would get back in. Even cabling route should not be ruled out. No way just atmosphere humidity would give isolation problems on a decent motor installation overnight. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Power-User
Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - New Member Technical Fields - Technical Writing - New Member Technical Fields - Education - New Member Fans of Old Computers - Apple II -

Join Date: Sep 2011
Location: Bellingham, WA
Posts: 191
Good Answers: 46
#10

Re: condensation problem in motor

01/15/2012 6:25 PM

One caution against using DC to warm the windings is that you might magnetically polarize the stator and rotor poles over time, leading to saturation when the motor is run on AC again. I once worked at an aluminum smelter where transformer-based arc welders were sometimes left in the potline room for long periods of time. The strong DC magnetic field of the potline would eventually magnetize the welder's iron core, rendering it unusable. When powered with AC, they would draw excessive current with every half-cycle because the core was magnetized in that direction, saturating at every other peak of the AC sine wave.

If something like this were to happen to your 11kv motor, it would ruin the motor!

For this reason alone, I would elect to use low-voltage AC (rather than DC) to warm the windings. The motor will be in a locked-rotor condition when warming, so there's no counter-EMF to contend with, meaning modest AC voltages should be all that are necessary to provide enough current to keep the stator warm and dry.

__________________
They call me "lightning" when wielding a hammer, because I never strike twice in the same place
Register to Reply Score 1 for Good Answer
Anonymous Poster #1
#11

Re: condensation problem in motor

01/15/2012 7:10 PM

ventilation might sovle the problem. try intalling a fan blade directly to the armature shaft. it might work if the motor runs continuously or short cycles. direct ventilation to the outside of the building in tandem with the armature fan should definately solve the problem.

Register to Reply
Active Contributor

Join Date: Nov 2006
Location: Ibadan, South Western Nigeria
Posts: 13
#12

Re: Condensation Problem in Motor

01/16/2012 3:21 AM

We have employed dehumidifiers to eliminate condensation in the store and to keep packaging materials from getting wet. This is less hazardous. It reduces down time. You may instal a localized humidifier and if your gadget is big enough, the whole enclosure could be dehumidified.

__________________
"Be cautious of a naked man who is offering to give you a shirt" olusojihercules53
Register to Reply
Active Contributor

Join Date: Oct 2011
Location: Tamworth, England, UK, Earth
Posts: 24
#13

Re: Condensation Problem in Motor

01/16/2012 5:58 AM

Spray it with WD40.

It works on wet spark plugs, leads and coils in car ignition systems.

__________________
No One's Dropped Dead Yet - Therefore It Must Be Safe
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14

Re: Condensation Problem in Motor

01/16/2012 6:18 AM

Has the task of lagging the pipes and tanks been completed? If not, then there is a process cooling load somewhere else just waiting to be saved....

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Nuclear Engineering - New Member

Join Date: Sep 2009
Location: Louisville, OH
Posts: 1925
Good Answers: 36
#15

Re: Condensation Problem in Motor

01/16/2012 4:17 PM

I agree with one poster who suggested that the humidity in the room needs to be addressed. An exhaust fan for the room may help.

However, IMO, you should not get condensation after only an hour even if the room humidity is quite high. The residual heat in the coils from running should not cool for several hours. I suspect something else is going on. My problem with condensation (vehicles stored in an unheated building) is when the temperature is rising and the humidity is high; this causes condensation on the cold metal when it doesn't warm up as fast as the room temperature. You should NOT get condensation, because the motors are warmer, plus the room temperature doesn't vary that much.

__________________
Lehman57
Register to Reply Score 1 for Good Answer
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#16
In reply to #15

Re: Condensation Problem in Motor

01/16/2012 4:32 PM

Exactly. That's why I suspected that water for some reason is already inside, and motor body can keep water from getting out equally well as from getting in. By the way, it should be obvious, but my phrase: water "cycles between phases" is about "water phases", not... electric phases. Hell, there goes a writer career. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#17

Re: Condensation Problem in Motor

01/18/2012 8:59 AM

Please make the motor installation place well ventilated. Also you may install several 400watt sodium vapor lamps just over the installed motor and the lamps will be in burning condition when the motor is not in operation. The heat generated by the lamps will keep the motor body in warm conditon and may prevent water condensation due fall of motor body temperature when not in operation. But before doing this, action should be taken to remove all entrapped moisture from the motor.

Also please check if there is any gap in the motor body, specially, in the terminal box,cable termination, etc, to prevent entry of the outside moistures.

Thanks,

Manindra

__________________
Manindra
Register to Reply
Register to Reply 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: