Leading Power Factor With 6.6 KV Motors

01/16/2012 11:18 PM

Energy meters connected with 6.6 KV motors, show lagging power factor at no load. But on full load of motors (7 motors connected at the output of 11/6.6 KV 2MVA Transformer), all energy meters show leading power factor. We have tried all possibility of reversal of phase sequence. The meters are CONZERV make and we are using more than 100 meters of same type/make. All other meters except this 6.6 bus section is working OK. I think there may be some problem with CT/PT direction, but tried all possible connections.

All are requested to guide please.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#1

Re: Leading power factor with 6.6 KV motors

01/17/2012 12:04 AM

Give description of motor(induction/synchronous etc) and type of starter.

__________________
pnaban
Register to Reply
Commentator

Join Date: May 2011
Posts: 61
Good Answers: 1
#2
In reply to #1

Re: Leading power factor with 6.6 KV motors

01/17/2012 12:13 AM

6.6 KV BHEL make Induction motor 175 KW and 250 KW with VCB

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4
In reply to #2

Re: Leading power factor with 6.6 KV motors

01/17/2012 9:32 AM

check the connections to the meter, if ok, replace the meter.

__________________
pnaban
Register to Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#3

Re: Leading Power Factor With 6.6 KV Motors

01/17/2012 9:08 AM

Are mechanical loads of these motors completely independent from other motors' ? If not, check their actual slip vs rated. You may be surprised by a minus sign. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Participant

Join Date: Nov 2011
Posts: 4
#5

Re: Leading Power Factor With 6.6 KV Motors

01/17/2012 10:54 PM

Just a thought: 1. Usually 6.6 KV loads for starting or stopping there would surge suppressors connected in parallel which consists of capacitors & Resistors. Check if any changes done recently. 2. The 6.6 KV motors do have capacitors fitted in the motor compartment, in case need to check any changes done. 3. What is the total load in KW, Amperes and actual voltage you would be able to workout your PF just to proof meters are reading correctly. Thanks.

Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#6

Re: Leading Power Factor With 6.6 KV Motors

01/18/2012 8:36 AM

What are the no-load currents and power factors of the motors? In general, in case of SQ. cage induction motor, the no-load current of the motor is restricted upto 40% of the full-load current of the motor.Also please check if capacitor banks are connected across the motor terminal for power factor improvement, the rating of the capacitor bank. Normally the capacitor bank rating would be maximum 90% no-load KVA of the motor. Next, by taking actual readings of KW consumption, Voltage acorss the motor terminal and current drawn by the motor actual power factor on-load can be calculated.

Thanks,

Manindra.

__________________
Manindra
Register to Reply