ABB VFD Drive ACS 800

01/16/2012 10:22 PM

What is the cause for DC Undervoltage trip for ACS 800 ABB VFD Drive, Once reset the trip indication it can start again?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: May 2011
Posts: 61
Good Answers: 1
#1

Re: ABB VFD Drive ACS 800

01/16/2012 10:55 PM

ACS 800 trips many times due to voltage dip in the system.

Case study:

AC drives (invertors) of ID and FD fans in New CPP trip as and when there was any voltage drop due to any fault in drown stream. Recent example is - Flash over in 33 KV line of Mehgao Mines on 14th Oct -10

We have activated Scalar flystart option of AC drives (ACS 800) of ID & FD fans of all three boilers to overcome this type of tripping.

In this mode, drives behave like a generator when ever any voltage dip occurs, for a pre defined period (1 sec in our case). Electronic circuit of the drive gets sufficient voltage, generated from motor, in case of any drop in line voltage. If line voltage does not get normalized within 1 sec, drive generates trip command.

Note: All these setting have been changed in consultation with ABB service engineer.

By : Satendra Kumar Tiwari, ACC Limited

Before implementing these settings at your equipment, expert advice is must

Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: ABB VFD Drive ACS 800

01/16/2012 11:12 PM

Here are the specs...it may need to be adjusted...

http://www.joliettech.com/abb_acs-800_ac_drive_specifications.htm

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: ABB VFD Drive ACS 800

08/23/2024 9:48 AM

One of the possibilities is that the supply cable(s) is/are undersized.

Refer to the relevant national electrical code, such as British Standard 7671, and assess.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

PWSlack (1); satendrakumart (1); SolarEagle (1)

Previous in Forum: Low Voltage in Outlet   Next in Forum: Leading Power Factor With 6.6 KV Motors

Advertisement