Low Voltage in Outlet

01/16/2012 5:47 PM

Ran into a problem with an outlet. Black (Hot) and White (Neutral) only show 90-95 Volts on my multimeter, while Black and Ground read 120-125. This drop happened suddenly and without applying any load at the time. Also I have no GCFI unit on that circuit and all other circuits run fine (dining room circuit). Only three outlets are on that circuit. I traced the problem to the first outlet and have the problem there. All neutral wires in the fuse panel box are tight (no loose connections).

I am at my wits end - any help is greatly appreciated.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#1

Re: low voltage in outlet

01/16/2012 6:15 PM

Check the voltage where the screws secure the wires, NOT into the plug. Pull the sockets from the wall and check then. 10:1 says you have a loose/burnt connection at one of the wall sockets.

Register to Reply
Power-User

Join Date: Oct 2010
Location: OZ, otherwise known as Oklahoma were the wind comes sweeping down the plains.
Posts: 159
Good Answers: 4
#9
In reply to #1

Re: low voltage in outlet

01/18/2012 9:43 AM

The receptacle may have the slip-in (piece of sh*t) terminals, if so turn off the circuit breaker, back the wire out of the slip-in terminal and put it in the screw terminal, tighten screw. Also, is the wiring copper or aluminum, if aluminum, make sure the receptacle is rated for aluminum or that copper pig tails have been properly installed.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: low voltage in outlet

01/16/2012 6:40 PM

If that doesn't work, I would disconnect both wires from both the outlet and the breaker box, with wires disconnected check continuity, if the wires are shorted you will get a reading, disconnect the outlets one by one until you find the culprit....If you don't get a reading tie the ends together on one end and check for continuity, if you don't get a reading the circuit is open...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#3

Re: low voltage in outlet

01/16/2012 7:37 PM

Almost certainly the neutral is disconnected somewhere. Your meter (bet it's a DVM) is picking up whatever's induced in the wiring.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Low Voltage in Outlet

01/17/2012 3:24 AM

....in which case measure the outlet voltage with a load plugged into it and turned on; 100W would do.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#5

Re: Low Voltage in Outlet

01/17/2012 11:35 PM

...... as DVMs are excellent in picking up stray field induced by nearby hot wire, into a now floating wire, making it look somewhat hot. Any real load (a lamp) precludes such a mistake.

Register to Reply
Guru
Australia - Member - New Member

Join Date: Jun 2011
Location: Thailand
Posts: 631
Good Answers: 3
#6

Re: Low Voltage in Outlet

01/18/2012 12:55 AM

You need to confirm that there is no load on the circuit - turn it off and see if any other devices lose power. Reason I ask, a friend had this problem - turned out that living near the sea, rust had created a high resistance connection in the common earth / neutral. (Not in the US)

Fridge (low impedance) was on one side of the centre earth circuit, his computer on the other side.

Fridge kicked in, low voltage across fridge, high voltage across (soon smoked) IBM.

Ground connections need checking.

__________________
Floss or die!
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#7

Re: Low Voltage in Outlet

01/18/2012 5:54 AM
Register to Reply
Power-User

Join Date: Apr 2010
Location: Moncks Corner, South Carolina, USA
Posts: 157
Good Answers: 6
#8

Re: Low Voltage in Outlet

01/18/2012 9:04 AM

Have you (or has anyone else) driven any nails lately?

__________________
You can always tell a Nuke because you can't tell him anything!
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#11
In reply to #8

Re: Low Voltage in Outlet

01/18/2012 10:51 AM

Great comment.

Maybe he "screwed up"?

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Apr 2009
Location: FL USA
Posts: 372
Good Answers: 9
#10

Re: Low Voltage in Outlet

01/18/2012 10:12 AM

Superb advice herein. Another diagnostic check is to load the last outlet in the set (100W lamp or so) and after a few minutes carefully finger check the face surface temperature of all outlets in the set. That 30V has to be dropping somewhere, and the power lost should show up as heat.

__________________
What is right is not always popular. - What is popular is not always right.
Register to Reply
Power-User

Join Date: May 2008
Location: Olympia, WA
Posts: 125
Good Answers: 5
#12

Re: Low Voltage in Outlet

01/18/2012 2:49 PM

Greetings.

It sounds like you are working on a high resistance open in the neutral.

This is tough. Old houses are plagued with this. We have 4,900 and most are older.

I have used analog and digital meters and even the voltage probes that you carry in your pocket but a neutral is sneeky and you can't find it easily.

The best that I have found is a "Wiggie" as my brother=in-law calls it.

It measures the voltage by amperage or load. I got one at Sears for less that $10.00. Wouldn't be without it.

Just find out what the circuit is and work backward.

I had one where the circuit went from one outlet to the other and they were slip ins (rotten way to do wiring) and I worked my way back and screwed in every wire until it worked.

Hope this helps.

Have a great day,

Oly

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#13

Re: Low Voltage in Outlet

01/18/2012 10:34 PM

Slip-ins??

I've never encountered such and it sounds like I've been blessed.

I've encountered some spring jawed connectors (not on outlets) but they required a lot more than a slip to get them in. They can bite hard enough to partially cut conductors which can then fail (open cct) under some conditions but that's another story.

Even without malignant slip-ins, it still sounds like you have a loose connector somewhere and, as others have beautifully suggested with some practical techniques, just needs finding and fixing...

Legacy domestic wiring can be a nightmare to untangle. Do you know the maintenance history of these premises?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Power-User

Join Date: Oct 2010
Location: OZ, otherwise known as Oklahoma were the wind comes sweeping down the plains.
Posts: 159
Good Answers: 4
#17
In reply to #13

Re: Low Voltage in Outlet

01/19/2012 8:21 AM

All of the duplex 15amp receptacles in my 1978 house were slip-in receptacles, they made it much quicker for the electrician to wire a new house. Cut, strip and stick, only tool needed was wire cutters.

Register to Reply
Power-User

Join Date: Jun 2008
Location: Kentucky Lake
Posts: 390
Good Answers: 26
#14

Re: Low Voltage in Outlet

01/19/2012 12:50 AM

Great answers, I can especially relate to the one about driving nails (is that the voice of experience I hear?). I think I could add screws, drill bits, and sawzall blades. Basically anything that penetrates the drywall will find a wire (unless of course, your looking for the wire).

I had this happen to my dishwasher. Burnt wire nut on the neutral in the DW's junction box. I never understood the less than line voltage reading I was getting at the controls, but now I understand it was due to induction. And I was indeed using a digital multimeter. I'm curious why this voltage reading would show only on a digital volt meter. Does an analog meter somehow dissipate that little bit of current produced through induction and indicate a correct reading of zero, the same way applying a load would?

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#15
In reply to #14

Re: Low Voltage in Outlet

01/19/2012 3:36 AM

In short, yes.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#16
In reply to #14

Re: Low Voltage in Outlet

01/19/2012 8:01 AM

The reason is that DVMs have often many hundreds of megohms impedance, a good analog meter has around 20,000 Ohms/Volt range....many far less.....some more......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Associate

Join Date: Dec 2011
Posts: 53
Good Answers: 2
#18
In reply to #14

Re: Low Voltage in Outlet

01/20/2012 12:03 PM

Yes, DVMs typically have 10 Megohms/volt or more internal resistance, while analog meters like the Simpson 260 have 40 Kohms/volt internal resistance. So the analog meter places a large enough load on the line to drain that induced voltage.

Register to Reply
Register to Reply 18 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (2); Barchetta (1); Fredski (1); Grand Poobah (2); JohnDG (2); leveles (1); nfhiggs (1); OlympiaWA (1); PWSlack (1); Rixter (1); SolarEagle (1); Stuart21 (1); U NO WHO (1); Wal (1); XNuke (1)

Previous in Forum: Cut Out Relay   Next in Forum: ABB VFD Drive ACS 800

Advertisement