Cost Comparison Power Transfer at Different Voltage Level

01/17/2012 5:16 AM

Want to know economics of 75 MW power transmission and distribution in a plant from Power plant ( 250 m Away from plant) at 33kV / 11 KV/6.6kV level. Which voltage level would b economical . Can you give a reough estimat or comparision?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#1

Re: Cost comparision Power transfer at different voltage level

01/17/2012 5:31 AM

Power= V x A, transmission at high current cost high due to bigger size of conductors, lessen the size of conductors, ideally you pick the higher voltage, that would be 33kV. Distance wont matter at all since from distribution line to corresponding consumer lines, distance would be considerably far enough so again cost wise, transfer of electrical energy should be at higher voltage with smaller conductor size. Thus also saving you the needs of step up-transformer, if you'd pick the lower Voltage rating at distrubution line for re-distribution to local consumers.

To further validate, do some comparative cost studies.

__________________
" To infinity and beyond" - Buzz Lightyear
Reply
Anonymous Poster #2
#2

Re: Cost comparision Power transfer at different voltage level

01/17/2012 6:02 AM
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Cost Comparison Power Transfer at Different Voltage Level

01/17/2012 11:56 AM

The higher the voltage the more current you get on a similar size conductor, to a point....That point being within the bounds of arc discharge, insulation, and other factors...

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4

Re: Cost Comparison Power Transfer at Different Voltage Level

01/17/2012 1:40 PM

Quote Eagle "The higher the voltage the more current you get on a similar size conductor"

Eagle, I think you have been on the beach too long. Sun has messed with your mind.

The higher the voltage the more power you can transfer. The current rating of the conductor is the same.

Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5
In reply to #4

Re: Cost Comparison Power Transfer at Different Voltage Level

01/17/2012 4:00 PM

Amps x volts = watts....The higher the volts times the same amount of amps equals a higher wattage ie; power ..If you want to maximize power, raise the voltage...I have solved the problem of getting more power over a small conductor many times by raising the voltage...I apologize for any misunderstanding

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#6

Re: Cost Comparison Power Transfer at Different Voltage Level

01/17/2012 6:15 PM

Eagle, I agree with you on that post 100%. I may have misunderstood your other post.