Could somebody please give me the reference, the calculation to select the conductor for overhead line? I mean, what formula is used to calculate the breaking load, before we could select, for example between AAC or AAAC?
You could probably google and find it but I would contact a cable mfg. They will likely have this information. Is this for a transmission line or distribution line?
Thanks all, but this is not for homework, but for a 20 kV distribution line :-)
I have found some reference, but they only calculates the sag and tension based on the selected conductor. I never done this before, but what client wants is calculation to get the minimum breaking load of conductor to select between AAC or AAAC.
I do not think you can calculate the breaking load. It is determined by test. I have a number of references that provide this information. Are you saying the spans are only 30 Meters? I would think the spans would be 100 meters. If so you have no concern. Will you experience heavy winds and ice accumulation on the conductor? If you sag the conductor to the MFG specs you won't have any problem. If you are still concerned use ACSR conductor.