Circuit Breaker Close And Open Coil Resistance Measurement

01/18/2012 3:42 PM

What do I have to use to measure the open and close coil resistance of the HV/MV circuit breaker control coils. Does regular ohm-meter do the accurate measurement (I mean because of the coil inductance?) or I have to use a ductor (micro-ohm) tester?

Thank you

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#1

Re: Circuit Breaker Close And Open Coil Resistance Measurement

01/18/2012 4:04 PM

What does your Instructor recommend? If you don't know, then your in over your head and shouldn't be troubleshooting the CB's. It could lead to disastrous results

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: Circuit Breaker Close And Open Coil Resistance Measurement

01/18/2012 9:03 PM

Modern CBs use μP based coils - be it Shunt Trip, Closing or UV coil. If your coils are of this type, you can't usually access the coil to measure its resistance.

Why do you need to measure it anyway?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Circuit Breaker Close And Open Coil Resistance Measurement

01/19/2012 5:38 AM

An Ohm-meter measures only the resistance because it does its measurement with a DC source inside the meter. So, it cannot mesaure any reactance. Whatever you read from an Ohm-meter is resistance only.

Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4

Re: Circuit Breaker Close And Open Coil Resistance Measurement

01/20/2012 8:59 AM

Typically, manufacturer's data on HV & MV breaker trip and close coils give a DC resistance value. You don't need to worry about the inductance. Most often they are DC powered in operation (not always, though!). Anyway, you should be able to meaure them with a DMM, because the value is usually give to tenths of ohms. Minor differences of 1 or 2 tenths of an ohm are not uncommon.

__________________