Selection of Nominal Voltage to Be Used

01/21/2012 2:03 PM

Given:

transformer UrTHV/UrTLV = 21kV/10.5kV selected nominal bus voltage of switchgear is Un=10kV

transformer UrTHV/UrTLV = 10kV/0.73kV selected nominal bus voltage of switchgear is Un=0.69kV

Is there any reason why switchgear nominal bus voltage is always selected lower than transformer rated secondary voltage? Any references?

thanks,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Sep 2009
Location: Singapore
Posts: 77
Good Answers: 1
#1

Re: Selection of nominal voltage to be used

01/21/2012 2:10 PM

As far as I know switchgear nominal voltage should be selected same to transformer rated voltage. While load voltage of switchgear shall be selected lower than switchgear nominal voltage to compensate voltage drop.

ex. transformer 13.8kV/0.48kv the switchgear must be selected Un=480volts while motor voltage connected to switchgear must be Urated=400V to compensate voltage drop.

Register to Reply
Anonymous Poster #1
#3
In reply to #1

Re: Selection of nominal voltage to be used

01/21/2012 11:41 PM

How much would the whole set of circuitry cost, compare to the switch?

I bet this Experienced User could explain

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#6
In reply to #1

Re: Selection of nominal voltage to be used

01/24/2012 6:04 AM

The secondary voltage you are referring to is the open circuit voltage of the trafo which will fall when load is applied on the secondary due to voltage regulation. This voltage (after loading) shall be the same as the rated bus voltage of the downstream switchgear.

Register to Reply
Commentator

Join Date: Sep 2009
Location: Singapore
Posts: 77
Good Answers: 1
#7
In reply to #6

Re: Selection of nominal voltage to be used

01/30/2012 1:44 PM

What if 90% is unloaded? Voltage will increase consequently switchgear will become overvoltage.

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#8
In reply to #7

Re: Selection of nominal voltage to be used

01/30/2012 11:37 PM

Yes. But that should not be a problem as the basic insulation level for the 480 V switchgear is 600V.

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Sep 2009
Location: Singapore
Posts: 77
Good Answers: 1
#9
In reply to #8

Re: Selection of nominal voltage to be used

01/31/2012 1:35 PM

I understand now why they call it 480V nominal voltage cause actual voltage may increase or decrease to nominal voltage that's why insulation level should always much higher than nominal voltage. thanks for sharing.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Selection of nominal voltage to be used

01/21/2012 5:00 PM

Do you get many motor burn outs?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#4

Re: Selection of nominal voltage to be used

01/22/2012 2:58 AM

What are the next up Un ratings?

Those ratings are pretty close to the service voltages.

Maybe the next ones up are (or were at time of build) just too much......?

Have they given you any grief?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Commentator

Join Date: Sep 2009
Location: Singapore
Posts: 77
Good Answers: 1
#5

Re: Selection of nominal voltage to be used

01/22/2012 10:02 AM

If switchgear is 480v and motor is 460volts the motor will not burn because we have 5% voltage drop on motor feeder ex. 480-(480x.05)=456v besides motor has +-10% voltage range. And in addition, 480volts bus switchgear in reality will have lower value than nominal because of voltage drop on upper stream unless if we adjust tap changer of transformer.

In IEC standard they use to make motor voltage equal to switchgear nominal voltage but transformer secondary voltage is higher than switchgear voltage.

ex.transformer UrTHV/UrTLV = 21kV/10.5kV selected nominal bus voltage of switchgear is Un=10kV

Trasformer and switchgear are almost on the same room, if actual voltage of secondary xformer is really 10.5kV then switchgear is undersized.

Any explanation why IEC do it like this?

Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); debata07 (2); jonald (4); TonyS (1); Wal (1)

Previous in Forum: Splicer Butler 1000 with DVG   Next in Forum: Alarm Logic

Advertisement