Why there is no Circuit breaker in Bus PT feeder?? In our system, interlock is given such that if any fault in Bus PT, then it opens the Incoming Bus breaker...Why it is done???Its 11kV busbar. Any economical problem in havng breaker for PT or its not necessary to have??? Kindly clarify
Re: Bus Potential Transformer feeder
01/25/2012 3:44 AM
Please post the single line diagram using the camera button.
India - Member - New Member Popular Science - Cosmology - New Member
01/25/2012 3:47 AM
When two or more transmission-line sections are connected to a common bus, a single set of potential transformers connected to the bus will generally have sufficient capacity to supply the protective-relaying equipments of all the lines. The provision of additional potential devices will quickly nullify the difference in cost.
Potential transformers energized from a bus provide a further slight advantage where protective-relaying equipment is involved in which dependence is placed on "memory action" for reliable operation. When a line section protected by such relaying equipment is closed in on a nearby fault, and if potential transformers connected to the bus are involved, the relays will have had voltage on them before the line breaker was closed, and hence the memory action can be effective. If the voltage source is on the line side of the breaker, as is usually true with capacitance potential devices, there will have been no voltage on the relays initially, and memory action will be ineffective. Consequently, the relays may not operate if the voltage is too low owing to the presence of a metallic fault with no arcing, thereby requiring back-up relaying at other locations to clear the fault from the system. However, the likelihood of the voltage being low enough to prevent relay operation is quite remote, but the relays may be slow.
Some people object to bus potential transformers on the basis that trouble in a potential transformer will affect the relaying of all the lines connected to the bus. This is not too serious an objection, particularly if the line relays are not allowed to trip on loss of voltage during normal load, and if a voltage-failure alarm is provided.
Re: Bus Potential Transformer Feeder
01/26/2012 2:16 AM
fuses are provided for pt as they are sufficient and at some places alarm provided as required for protection system
sbwad
01/27/2012 11:31 AM
Sorry if I have asked you in wrong manner. ie. I referred to 11kV Switchgear panels of Unit, Station Transformer.Kindly find below the snapshot of the part of feeder.Hope it is enough for you to rectify my doubt.
02/07/2012 2:47 AM
so
u need to consider
"whether fuse is more compatible and cost efficient than the breaker"
and then u will get the answer.