Reading Between Earth and Neutral 120V

01/27/2012 11:46 AM

Hi

Could any body help, the reading between earth and neutral in the incomer supplying power to the house is 120V while live and neutral reads normal 220V and live-earth reads up to 298V that is utility power supply. When generator running, no load voltage is normal 220V, but when load connected, the reading between live and neutral shoot to 400V and cause damage to domestic appliances.

Regards

Mtonyole

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Reading Between Earth and Neutral 120V

01/27/2012 12:46 PM

Where about in the world are you, it may give us a clue to what should be your normal supply voltage.

To be honest I would be getting the supply company involved.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#2
In reply to #1

Re: Reading Between Earth and Neutral 120V

01/27/2012 4:18 PM

And, are you saying you have a generator connected in addition to the incoming utiliity?

Register to Reply
Power-User

Join Date: Aug 2007
Location: San Francisco Bay Area
Posts: 266
Good Answers: 21
#3

Re: Reading Between Earth and Neutral 120V

01/27/2012 7:09 PM

Mtonyole,

Sounds like an open neutral somewhere.

Hire a qualified and experienced electrician to find and correct it.

__________________
Speed doesn't kill. Sudden stops, brick walls, and old ladies in Buicks do.
Register to Reply
Commentator

Join Date: Sep 2011
Location: Durban South Africa
Posts: 75
Good Answers: 2
#4

Re: Reading Between Earth and Neutral 120V

01/28/2012 12:46 AM

dmtonyole

You have a floating neutral. That is an earthing problem which manifests as a neatral voltage above earth potential. An assymetrical neatral point in the three phase system. Thats why when the generator is running unloaded all is well until you connect your assymetrical load. Get a qualified electrician to sort it out...chop chop.

Register to Reply
Participant

Join Date: Dec 2011
Posts: 1
#5

Re: Reading Between Earth and Neutral 120V

01/28/2012 1:42 AM

Hi dmtonyole,

I agree to the two previous comments, you have a floating or loss connection neutral cable, causing high and abnormal voltage. I experience this several times in our huge site & I told to my electrician to check & re-tight all neutral terminal from the whole circuit, & they were found loss connection after tightening the power supply back to normal.

regards

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Reading Between Earth and Neutral 120V

01/28/2012 3:25 AM

Yep. The neutral is broken somewhere upstream of the user connection.

The 400V thing merely indicates the generator and the utility supply are out-of-phase.

It's a utility company distribution network problem, which needs sorting without any delay. Do not use the installation until the problem has been sorted out.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Nov 2011
Posts: 4
#7

Re: Reading Between Earth and Neutral 120V

01/28/2012 4:46 AM

My thoughts for you: 1. Incoming supply could be from star connected system and may be neutral earthing defective. 2. Severely unbalanced load could cause floating neutral 3. Your generator neutral not effectively earthed. 4. Check all earthing system to ensure no loose connections.

Register to Reply
Power-User

Join Date: Apr 2007
Posts: 414
Good Answers: 19
#8

Re: Reading Between Earth and Neutral 120V

01/28/2012 8:47 AM

If this is an old building, the wiring may not comply with the modern requirement of a continuously grounded neutral. In another life my workplace was a converted house built in 1880, with the original wiring. There was a 120-240 volt single phase electric service, and all three lines were fused.

One day, the fuse on the conductor connected to the "neutral" blew. Some of the lights in the building got very dim, and the rest were burning much too brightly. Some light bulbs and small appliances just gave up the ghost.

Don't let this happen to you. Call a qualified electrician.

Register to Reply
Commentator

Join Date: Dec 2006
Posts: 77
#9
In reply to #8

Re: Reading Between Earth and Neutral 120V

01/30/2012 12:02 AM

Hi

Thanks for your comments, the problem of neutral reading 120V were resolved by utility power supply company, there was a problem in the transformer. The generator still supply over voltage when loaded, we will check if all connections are tight.

Regards

Mtonyole

Register to Reply Off Topic (Score 5)