Anonymous Poster

3-Phase to 1-Phase Amperage Draw

05/03/2007 10:37 AM

I would like to know what the amperage draw would be for a 2000 watt heater

at 208v 1 phase and at 208v 3 phase.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#1

Re: 3 phase to 1 phase

05/03/2007 10:48 AM

Single Phase Watts = Volts x Amperes x Power Factor

Three Phase Watts = Volts x Amperes x Power Factor x 1.732

Reply
Anonymous Poster
#2

Re: 3-Phase to 1-Phase Amperage Draw

05/03/2007 2:34 PM

Single phase at 208v = 9.6A

Three phase at 208v = 5.54A

Reply
Anonymous Poster
#3
In reply to #2

Re: 3-Phase to 1-Phase Amperage Draw

05/03/2007 3:08 PM

Thank you for your responses.

Reply
Anonymous Poster
#4

Re: 3-Phase to 1-Phase Amperage Draw

05/04/2007 2:09 AM

single phase= 2000/208

three phase= 2000/208/3

assume heaters are resistive not inductive nature

Reply
Anonymous Poster
#5

Re: 3-Phase to 1-Phase Amperage Draw

05/04/2007 5:43 AM

To adapt this heater between single phase and three phase, it would require 3 separate elements which are assumed to be resistive so there is no Cos component involved in the calculation.

In single phase mode the three separate elements would be combined in parallel with a total load of 2000W/208V = 9.6A.

Because you are quoting a 3 phase Line voltage of 208V which is the same as the phase voltage, the resistance/voltage relationship per phase is equivalent to one element at 65ohms and as there is no benefit of a higher voltage on the three phase supply then the phase current is the same 208/65 = 3.2A per phase.

When the higher voltage is not applicable the 1.732 component does not apply.

Did you mean to state 208V - 3 phase?

Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#6

Re: 3-Phase to 1-Phase Amperage Draw

05/04/2007 8:22 AM

Uh . . . At what voltage is the heater rated for 2000 W? If it's a 240 V heater rated at 2000 W, then it won't put out 2000 W at 208 V. 208 V is 208 V whether it's 1 phase or 3 phase.

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply
Anonymous Poster
#7

Re: 3-Phase to 1-Phase Amperage Draw

05/05/2007 5:43 AM

Bill is correct.

The element resistance is designed according to the rated design voltage of the equipment and the correct answer to your question requires the original rated voltage.

Your other replies are also correct - on the basis of your information the single phase current is 9.6A

If the element is Star connected to a 3 phase -4 wire supply, then the phase current is 3.2A

If the elements are Star connected to a 3 phase 3 wire supply the phase current will be 1.85A

If the elements are Delta connected to a 3 phase 3 wire supply the current will be 5.5A.

Reply