Can any one tell me what is the IEC standard distance for laying two single core cable 110 kV circuits in a same trench in trefoil or flat formation and which bonding method will be more appropriate?
Re: Spacing Between Two 110 kV Single Core Circuits in a Trench
01/30/2012 8:54 AM
I'm sure that somebody can tell you this standard, if it exists. A better question for you here will be which IEC standard has this information, so you can buy the correct standard? I do not work with IEC standards. I work with NEC, NFPA standards so I cannot tell you which to purchase.
01/31/2012 4:58 AM
thanx for your reply,do you know any such standard for NEC or NFPA.
01/31/2012 3:01 AM
Where I work I have transformer station 400kV/110kV that is being retrofitted,from air insulated switchgear to gas insulated switchgear 110 kV. The connections for the power lines are made using 500mm2 XLPE cable layed in a trench, 450mm between each power line, 1000 mm between power line and 110 kV transformer connection and 1500 mm between two transformer connections.The cable for transformer is 2000mm2.
These distances were taken from a national norm for power lines, addapted after the IEC standards.
Try this for more info:
http://www05.abb.com/global/scot/scot245.nsf/veritydisplay/ab02245fb5b5ec41c12575c4004a76d0/$file/xlpe%20land%20cable%20systems%202gm5007gb%20rev%205.pdf
and
http://www.nexans.no/eservice/Norway-no_NO/fileLibrary/Download_540199654/Norway/files/Underground_power_cables.pdf
cheers
nikolay
The time is ......now
02/01/2012 10:39 AM
There is no IEC Standards for what you asked.
The Utility/Main Contractor shall decide the formation and bonding method based on the required load, the cable manufacturer shall design the cable based on the received information such as:
a) Transmitted Power (Load) b) Ground temperature (max).
c) Soil Thermal resistivity.
d) Depth of laying
e) Total number of cable/circuit in groups
You may refer to this catalogue for more information: