Spacing Between Two 110 kV Single Core Circuits in a Trench

01/30/2012 8:29 AM

Can any one tell me what is the IEC standard distance for laying two single core cable 110 kV circuits in a same trench in trefoil or flat formation and which bonding method will be more appropriate?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Spacing Between Two 110 kV Single Core Circuits in a Trench

01/30/2012 8:54 AM

I'm sure that somebody can tell you this standard, if it exists. A better question for you here will be which IEC standard has this information, so you can buy the correct standard? I do not work with IEC standards. I work with NEC, NFPA standards so I cannot tell you which to purchase.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Member

Join Date: Jan 2012
Posts: 8
#3
In reply to #1

Re: Spacing Between Two 110 kV Single Core Circuits in a Trench

01/31/2012 4:58 AM

thanx for your reply,do you know any such standard for NEC or NFPA.

Register to Reply Off Topic (Score 5)
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#2

Re: Spacing Between Two 110 kV Single Core Circuits in a Trench

01/31/2012 3:01 AM

Where I work I have transformer station 400kV/110kV that is being retrofitted,from air insulated switchgear to gas insulated switchgear 110 kV. The connections for the power lines are made using 500mm2 XLPE cable layed in a trench, 450mm between each power line, 1000 mm between power line and 110 kV transformer connection and 1500 mm between two transformer connections.The cable for transformer is 2000mm2.

These distances were taken from a national norm for power lines, addapted after the IEC standards.

Try this for more info:

http://www05.abb.com/global/scot/scot245.nsf/veritydisplay/ab02245fb5b5ec41c12575c4004a76d0/$file/xlpe%20land%20cable%20systems%202gm5007gb%20rev%205.pdf

and

http://www.nexans.no/eservice/Norway-no_NO/fileLibrary/Download_540199654/Norway/files/Underground_power_cables.pdf

cheers

nikolay

__________________
The time is ......now
Register to Reply
Member

Join Date: Feb 2012
Posts: 6
#4

Re: Spacing Between Two 110 kV Single Core Circuits in a Trench

02/01/2012 10:39 AM

There is no IEC Standards for what you asked.

The Utility/Main Contractor shall decide the formation and bonding method based on the required load, the cable manufacturer shall design the cable based on the received information such as:

a) Transmitted Power (Load) b) Ground temperature (max).

c) Soil Thermal resistivity.
d) Depth of laying
e) Total number of cable/circuit in groups


You may refer to this catalogue for more information:

http://www.nexans.no/eservice/Norway-no_NO/fileLibrary/Download_540199654/Norway/files/Underground_power_cables.pdf

Register to Reply
Register to Reply 4 comments
Copy to Clipboard

Users who posted comments:

Aamir Arshad (1); Firas Atwan (1); nikolay (1); redfred (1)

Previous in Forum: PLC   Next in Forum: Stator Earth Fault for High Voltage Generator

Advertisement