Stator Earth Fault for High Voltage Generator

01/30/2012 10:00 AM

I gatta such indication in 11MW HV generator during synchronization time, as result we could not be able to synchronize machine....after troubleshoot we came to conclude maybe Lightening Arrestor or Voltage Transformer(Ground transformer ) maybe defective...could someone tell me what to do ???how can we test 9KV Lightning Arrestor???or someone can suggest what possibly causes as per entitled subject.

VOLTAGE TRANSFORMER DETAILS

1 PHASE, 50VA/ Phase

Class BZ

Ratio 6350/110V

Line Voltage=6350

serio no:RVB 349017

LIGTNING ARRESTOR DETAILS

9KV

50/60 Hz

DUTY CLASS

10KA

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: STATOR EARTH FAULT FOR HIGH VOLTAGE GENERATOR

01/30/2012 10:11 AM

The thing to do is to read the manual, then pick up the telephone, and ring the equipment manufacturer's technical helpline.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Associate

Join Date: May 2011
Location: Los Angeles, Ca.
Posts: 35
Good Answers: 1
#2

Re: Stator Earth Fault for High Voltage Generator

01/30/2012 12:49 PM

The Lightening arrestor can be checked with and ohm meter an should be wide open. That is the simplest. The better way is to put an amp meter& arrestor in series with a dc voltage source and bring the voltage up slowly. If you get any current, shut it off because it's broken. If you attain your operating voltage without current draw it's probably OK. This of course does not check for spikes or surges. For them you must go higher.

__________________
Life long learning in an endless universe of possibilities! Just go for it!
Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3
In reply to #2

Re: Stator Earth Fault for High Voltage Generator

01/31/2012 8:32 PM

A conventional ohmmeter (or DMM) isn't going to be able to diagnose the OP's problem if he actually has stator insulation breakdown going on, unless it's practically a bolted fault to ground. What he needs is to do a DC insulation resistance test with an instrument made for that purpose, usually called a "megger" or megohm meter.

For the voltage rating of his equipment, he should use at least a 5000V megger. Test the stator insulation to ground with all other items disconnected (including disconnect the neutral grounding transformer and the arresters). Test the neutral grounding transformer from primary winding to ground and primary to secondary winding (at 5000V) and secondary winding to ground (at 500V). Test the arresters to ground at 5000V.

These are the simplest tests to perform, and will show most gross problems. If they all come out okay, then more diagnostics are needed, such as is the stator ground relay set properly and operating properly, is the resistor on the neutral transformer secondary the proper value (or exists at all), and so on. This will need the services of a qualified HV testing company, which is the OP's best course of action anyway.

__________________
To get the right answers, first you need to ask the right questions.
Reply
Anonymous Poster #1
#4

Re: Stator Earth Fault for High Voltage Generator

02/03/2012 6:25 AM

do you know recommanded setting (ISO based lists of differents generators ratings and trasformers ???it will help me in future problem.My generator has 12.5 MVA with neutral grounding transformer of proximate 9kva ) after Meggering using 5000kv or any other megger.????when u troubleshoot earthling fault at stator terminals(ie neutral grounding transformer and Lightening arrestor or some generator low resistance maybe used) of generator.

Reply
Associate

Join Date: May 2012
Posts: 52
#5

Re: Stator Earth Fault for High Voltage Generator

05/16/2012 1:03 AM

synchronized connection is easy just connect the the genset to the MCB bus bar togehter with the national public power then your done !!! and to make an automatic trasfer you need to get or install automatic transfer switch and for installing the autotrasfer switch the line/ neutral cable connect to the genset line / neutral so when the genset will shutdown the autotrasfer switch will closed he will trigger the contactor to swift in national power . but if you are not qualified to do the job just call me oppppssss!!! not me call your eletrician,

__________________
i want ot helf piple need assistance and to share my knowleged in technical
Reply