01/30/2012 3:07 PM
i wanna know what is the difference between iu and in. i have a circuit breaker that has the following nameplate in=63 A , iu= 160A
Re: circuit breaker rating
01/30/2012 3:29 PM
If you want an accurate answer without any guessing I'd look at the manufacturer's website for application notes and your specific part specifications.
01/30/2012 4:04 PM
in=63A is the max current at specified temp, and I believe that the iu=160A is probably short circuit max current, but I could be wrong..
Re: Circuit Breaker Rating
01/30/2012 4:56 PM
Good Answers: 804
01/30/2012 6:13 PM
From IEC 60947-3
Rated uninterrupted current (Iu)
The rated uninterrupted current of an equipment is a value of current, stated by the
manufacturer, which the equipment can carry in uninterrupted duty.