Hello folks,
I work at an embedded electronics based design house. Since we are a design house, we come across many fields of engineering, most of which are not our forte. But this provides us a lot of technical exposure and learning.
One of our clients recently got back to us regarding a problem that he is facing in the field. He is also a voltage stabilizer manufacturer and uses relays to switchover winding-tappings on an auto transformer to maintain the output voltage. Most relays get damaged due to arcing in over an year's time. Since he is an old client we agreed to analyze his problem. We were working on digitizing his stabilizer using triacs as a solution to replace the relays and hence did not focus on the relay issue.
The present analog Stabilizer solution he has, is sold by him at about USD 50-60 and e cannot afford an overburden of 5-10 USD on his existing cost.
The Stabilizer is used on the 230VAC, 50Hz supply(India), and is rated for 5KVA. It operates from 90VAC to 265VAC regulating the output Voltage to 195 to 245VAC. The client uses 24V single-pole double throw relays, three relays to change the input tappings, one relay to change the output tapping and a 24V single-pole single throw relay for cutting off or making the output voltage.
We observed that in one of the input winding changing relays,
- the Voltage across the NO(Normally-Open) and C (common) is always within 0 to 40V peak AC during normal operation
- the Voltage across the NC(Normally-Closed) and the C varies from 0 to 40V peak AC.
- the current flowing through the circuit (in test condition with 600W/250V incandescent lamp resistive load) is 2.2A rms.
- During relay changeover the voltage across the relay terminals rises up-to 200VAC, on occasions there is a one cycle peak current of about 5 to 30 A AC.
- An arc is generated at the NC contact wile breaking and at the NO contact while making contact. (also the other way around, but these arcs are more prominent). The breaking arc at the NC lasts longest (5 to 10ms). The making arc usually lasts from 1 to 3ms.
We tried to adding snubbers and also varistors.With 60V Varistors the voltage is arrested at ~60VpeakAC. the current also seems to stay within a 3A AC margin. But in-spite of this there still exists an ARC during making and breaking. We were baffled that an arc so profound could be generated at 40VAC and 2.5A AC.
Though the test load was resistive type 600W, the actual implementation may experience inductive loads with PF 0.6 onwards @4KW. meaning around 16 to 35A AC depending on the input voltage. That is really scarry as far as I am concerned.
I tried searching online and also on CR4, but none seem to address the particular issue.
We have contemplated many solutions, of which we have ruled out the option of having the solutions which include a diode, as the diodes become extra-ordinarily costly for the current rating that the client has. Or am i wrong in considering the diode current for a snubber ckt, where the configuration is:
ContactA<->1diode|>|<->1capacitor<->ContactB
ContactA<->1diode|<|<->1capacitor<->ContactB
with a resistor across the two Capacitor-diode junction for charge dissipation.
Two such circuits for each relay (NC - C jn and NO - C jn) are required.
Is is possible that I am going wrong somewhere in analyzing the situation at hand or in interpretting the current through the diode.
Other option at hand is RC combination circuits, but cannot seem to determine the values. Will start to experiment with RC values about tomorrow and will keep updating.
Would appreciate any suggestions at handling the system.
Would be overwhelmed if responded to, by someone who has practically faced these scenarios.
with regards,
Vishal Vijay Singh
P.S.:
- My apologies for being verbose, bu i figured that better to provide maximum information to start with rather than providing rebuttals and corrections later. :)
- Dear Admin.. I have listed this thread in the electrical section, if u find it suits instrumentation better then kindly change or direct me as necessary.