ARC Quenching - Single-Pole Double-Throw Relay

01/31/2012 8:24 AM

Hello folks,

I work at an embedded electronics based design house. Since we are a design house, we come across many fields of engineering, most of which are not our forte. But this provides us a lot of technical exposure and learning.

One of our clients recently got back to us regarding a problem that he is facing in the field. He is also a voltage stabilizer manufacturer and uses relays to switchover winding-tappings on an auto transformer to maintain the output voltage. Most relays get damaged due to arcing in over an year's time. Since he is an old client we agreed to analyze his problem. We were working on digitizing his stabilizer using triacs as a solution to replace the relays and hence did not focus on the relay issue.

The present analog Stabilizer solution he has, is sold by him at about USD 50-60 and e cannot afford an overburden of 5-10 USD on his existing cost.

The Stabilizer is used on the 230VAC, 50Hz supply(India), and is rated for 5KVA. It operates from 90VAC to 265VAC regulating the output Voltage to 195 to 245VAC. The client uses 24V single-pole double throw relays, three relays to change the input tappings, one relay to change the output tapping and a 24V single-pole single throw relay for cutting off or making the output voltage.

We observed that in one of the input winding changing relays,

  1. the Voltage across the NO(Normally-Open) and C (common) is always within 0 to 40V peak AC during normal operation
  2. the Voltage across the NC(Normally-Closed) and the C varies from 0 to 40V peak AC.
  3. the current flowing through the circuit (in test condition with 600W/250V incandescent lamp resistive load) is 2.2A rms.
  4. During relay changeover the voltage across the relay terminals rises up-to 200VAC, on occasions there is a one cycle peak current of about 5 to 30 A AC.
  5. An arc is generated at the NC contact wile breaking and at the NO contact while making contact. (also the other way around, but these arcs are more prominent). The breaking arc at the NC lasts longest (5 to 10ms). The making arc usually lasts from 1 to 3ms.

We tried to adding snubbers and also varistors.With 60V Varistors the voltage is arrested at ~60VpeakAC. the current also seems to stay within a 3A AC margin. But in-spite of this there still exists an ARC during making and breaking. We were baffled that an arc so profound could be generated at 40VAC and 2.5A AC.
Though the test load was resistive type 600W, the actual implementation may experience inductive loads with PF 0.6 onwards @4KW. meaning around 16 to 35A AC depending on the input voltage. That is really scarry as far as I am concerned.

I tried searching online and also on CR4, but none seem to address the particular issue.

We have contemplated many solutions, of which we have ruled out the option of having the solutions which include a diode, as the diodes become extra-ordinarily costly for the current rating that the client has. Or am i wrong in considering the diode current for a snubber ckt, where the configuration is:

ContactA<->1diode|>|<->1capacitor<->ContactB

ContactA<->1diode|<|<->1capacitor<->ContactB

with a resistor across the two Capacitor-diode junction for charge dissipation.

Two such circuits for each relay (NC - C jn and NO - C jn) are required.

Is is possible that I am going wrong somewhere in analyzing the situation at hand or in interpretting the current through the diode.

Other option at hand is RC combination circuits, but cannot seem to determine the values. Will start to experiment with RC values about tomorrow and will keep updating.

Would appreciate any suggestions at handling the system.

Would be overwhelmed if responded to, by someone who has practically faced these scenarios.

with regards,

Vishal Vijay Singh


P.S.:

  • My apologies for being verbose, bu i figured that better to provide maximum information to start with rather than providing rebuttals and corrections later. :)
  • Dear Admin.. I have listed this thread in the electrical section, if u find it suits instrumentation better then kindly change or direct me as necessary.
__________________
I would like to be a human in true sense one day...
Register to Reply
Pathfinder Tags: arc arc quenching Relay Snubber
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: ARC Quenching - Single-Pole Double-Throw Relay

01/31/2012 10:27 AM

Refreshing to see a well-framed question in these days when many 'wot dat?' posts are seen daily.

You should search for a Tyco document called 'Tyco_v4bg_4.pdf' which i can't find anymore, pity. If you can't either, send me a private mail message using the CR4 pm system, giving your email id, and i will send the document. It may give some helpful tips to you.

Is the client using both NO and NC of one set of contacts? If so, it is asking for trouble. He must use 'potential-free' contacts. Just my two cents.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: May 2006
Location: Chennai - India
Posts: 103
#4
In reply to #1

Re: ARC Quenching - Single-Pole Double-Throw Relay

01/31/2012 11:52 AM

Thank you Mr. Sridhar for your suggestion.

But in our case it is imperative to avoid the 2 potential situation as the relays are used to switch-over the voltage from one stage to another by changing the input-winding contact point.

Each relay requires upto 8ms energising time and the change-over action takes about3-8ms. So the system is so designed that at any point in time only one relay be operated to cause change in voltage. If 2 individual relays were used to cause the make and break, there could either be discontinuity in the Voltage//Current AC or it may cause bucking of the windings by temporarily shorting a winding of the auto-transformer.

Hence we are moving forward to triacs for their new design, but triacs also have their own inherent problems (lets leave triacs alone for another day of reckoning ;) ).

The client would like to know if the arcs can b reduced to aid them in reducing the problem in their old design.

Does it become difficult to control the arc when both NO and NC are carrying a potential?

regards,

Vishal...

__________________
I would like to be a human in true sense one day...
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5
In reply to #4

Re: ARC Quenching - Single-Pole Double-Throw Relay

01/31/2012 12:09 PM

Firstly, yes, if you use both NC and NO of a changeover contact, you must ensure that there is no inductive load, since persistent arcs can cause havoc. So the US insistence on potential-free contacts makes sense usually.

Arcs can be controlled to some extent by using (a) RC networks, (b) freewheeling diodes (DC only) and (c) MOVs across the break. Explained in that Tyco document. Please give me your personal mail id if you want that document... i am repeating myself, sorry.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User

Join Date: May 2006
Location: Chennai - India
Posts: 103
#14
In reply to #5

Re: ARC Quenching - Single-Pole Double-Throw Relay

02/01/2012 1:58 AM

I am not sure if this information is relevant, forgot to mention earlier. The common point is the potential carrier/supplier. The moving contact establishes the contact to 2 winding segments at different points of time.

The windings are part of an auto-transformer whose one end is connected to the Neutral line of the mains input supply. The phase is linked and provided by the choice of relay, similar to a daisy chain arrangement.

During transition(when moving contact is physically not in contact with the NC or the NO) the potential of the winding end, the NO and the NC becomes same as the Neutral(drops to 0) while the moving contact is held at phase potential. This is what causes me to observe a 150 to 250V AC odd voltage between the NO and C and also NC and C. So I guess providing Varistors was the worst idea ever as it would cause the winding connected to the NO and NC to buck or short-circuit. This is my assumption from the observation made. I'll post the images soon.

So I guess the varistor//thermistor based snubbing is out of the window for me.

Rather should now try the RC combination snubbing... But I am more concerned about the diode current rating selection as discussed earlier in my posted question. It would be great help if someone could guide me in determining the diode current for use in the snubber circuit.

regards,

Vishal...

__________________
I would like to be a human in true sense one day...
Register to Reply
Power-User

Join Date: Apr 2007
Posts: 414
Good Answers: 19
#12
In reply to #1

Re: ARC Quenching - Single-Pole Double-Throw Relay

02/01/2012 12:44 AM

I couldn't find "Tyco_v4bg_4.pdf" either, but since Tyco Electronics is now TE Connectivity there may be something on this website:

http://www.te.com/en/home.html

I found some devices of the type here. Don't give up searching online. You never know when lightning will strike.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#17
In reply to #12

Re: ARC Quenching - Single-Pole Double-Throw Relay

02/01/2012 2:34 AM
__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User

Join Date: May 2006
Location: Chennai - India
Posts: 103
#20
In reply to #17

Re: ARC Quenching - Single-Pole Double-Throw Relay

02/01/2012 2:49 AM

Thank you both for the document... Will read and get back..

__________________
I would like to be a human in true sense one day...
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#2

Re: ARC Quenching - Single-Pole Double-Throw Relay

01/31/2012 10:32 AM

You tried magnetic arc suppression?

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Power-User

Join Date: May 2006
Location: Chennai - India
Posts: 103
#3
In reply to #2

Re: ARC Quenching - Single-Pole Double-Throw Relay

01/31/2012 11:36 AM

We did speculate that option but could not come to terms with the location of the magnets or how to ensure an attraction or deflection of the arc.

My BAD.. I should have explained the relay in-detail as well.

The relay is a standard 40 to 50A relay, (Wires can be screwed on the terminals. Not a PCB mount or Panel mount type.)

The distance between (not referring to the terminals) the static contactors and the moving contact in either position is 2-3mm. The relay dimension is 30mmx40mmx60mm.

There doesn't seem to be a provision for fixing the magnet close enough with out endangering electrical safety of the equipment.

The rough cost of each relay is about USD1.

Thanks for the suggestion though.. And if possible do suggest how I may be able to successfully mount the magnet and what strength would be required to deflect upto 4A to start with. And the actual current flowing in the circuit can reach upto 45A.

with thanks and regards,

Vishal...

__________________
I would like to be a human in true sense one day...
Register to Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#6

Re: ARC Quenching - Single-Pole Double-Throw Relay

01/31/2012 4:03 PM

Snubbers and arc suppression are now ancient history to me and my input there would be out of date.

However, I may be able to give some suggestion on what might be the arc source even with resistive load. You describe this as a "tap changing" system and so the source may be either the transformer coils themselves, depending on the structural configuration you have.

__________________
Just an Engineer from the land down under.
Register to Reply
Power-User

Join Date: May 2006
Location: Chennai - India
Posts: 103
#18
In reply to #6

Re: ARC Quenching - Single-Pole Double-Throw Relay

02/01/2012 2:36 AM

Hi. thank you for ur responce.

The source is not a worry at all. I am more concerned with the snubber design.

Though outdated as per ur consideration, ur outdated information could still b new information to me. So dont bother and bring it on.. :)

thanks again...

__________________
I would like to be a human in true sense one day...
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15603
Good Answers: 982
#7

Re: ARC Quenching - Single-Pole Double-Throw Relay

01/31/2012 4:57 PM

The implication that you are switching the taps of a transformer is a big hint. Regardless of the final load being a resistive load, on transition there will always be a reactive component. Since you are switching an AC signal, the standard practice of a Flyback diode across the inductive load will not work. I suspect your best solution will be a careful consideration of relay contact opening and closing times. The phrase "make before break" instead of the traditional "break before make" should be for one of your relays in this switching process. This will likely require more relays/contactors than you're using now but this is a common solved problem using these relays.

I cannot remember which CR4 member recently explained a schematic diagram here that had these types of relays. But I think this approach solves any current lag switching of reactors.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#10
In reply to #7

Re: ARC Quenching - Single-Pole Double-Throw Relay

01/31/2012 8:12 PM

I think Redfred is on the right track. It is worth looking into the principles used in power transformer on-load tap changers. There is lots of info online about how they work, and you can probably adapt their principles to your smaller-scale application. See the following link in Wikipedia for an animated example:

http://en.wikipedia.org/wiki/Tap_(transformer)#Mechanical_tap_changers

By overlapping the operation of your relays and using a snubber of some sort on the main switching relay(s), you can significantly reduce the stress on at least most of your relay contacts. Since your relays are operated electrically rather than mechanically, some of the (loss of) timing issues that usually cause failure of mechanical tap changer contacts can be eliminated.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: ARC Quenching - Single-Pole Double-Throw Relay

01/31/2012 5:11 PM

If you are switching transformer coils, it's likely an inductive kickback issue. The first line of defense is a diode across the inductor coil.

http://www.coilgun.info/theoryinductors/inductivekickback.htm

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15603
Good Answers: 982
#9
In reply to #8

Re: ARC Quenching - Single-Pole Double-Throw Relay

01/31/2012 6:01 PM

But your coil gun link refers to DC applied across an inductor being removed not AC across an inductor. With an AC voltage the diode will be forward biased and by passing the inductor for half of the cycle.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User

Join Date: May 2006
Location: Chennai - India
Posts: 103
#16
In reply to #9

Re: ARC Quenching - Single-Pole Double-Throw Relay

02/01/2012 2:33 AM

A possible configuration is discussed in my question itself. Also another way of using it is 2 back to back TVS diodes of a voltage rating that we need to clamp to.

The bigger issue is the rating selection of these diodes.

vishal...

__________________
I would like to be a human in true sense one day...
Register to Reply
Power-User

Join Date: May 2006
Location: Chennai - India
Posts: 103
#23
In reply to #9

Re: ARC Quenching - Single-Pole Double-Throw Relay

02/01/2012 4:38 AM

The exact configurations do not help but diodes can be used in parallel to the switching point along with a voltage limiting circuit. but the bigger issue for me is in determining the current requirement or rating of the diode.

regards

Vishal...

__________________
I would like to be a human in true sense one day...
Register to Reply
Power-User

Join Date: May 2006
Location: Chennai - India
Posts: 103
#15
In reply to #8

Re: ARC Quenching - Single-Pole Double-Throw Relay

02/01/2012 2:23 AM

As posted in the question i do intend to use the diode but am not able to determine of what rating it should be to perform the operation without burning or burning a hole in the pocket ;)..

Thanks..

Vishal...

__________________
I would like to be a human in true sense one day...
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#11

Re: ARC Quenching - Single-Pole Double-Throw Relay

01/31/2012 11:47 PM

IMHO this design will never work good enough. The steps are pretty big and the switching lacks intelligence, it is depending on "luck" only (read switch- response time, reaction time or name it)

Connect an oscilloscope and measure what "really" happens. You will have spikes that can reach to 2 times the voltage. (I try to translate, we call it reverse voltage, because of the frequency vs. alternance) With relays, you cannot switch cutting through the zero points of a period like is done with power controls. (too slow)

The make before- break theory is correct, - look at a rheotor autotransformer with a sliding contact on the circumference. The "brush" is made to overlap part of the next (or previous on the way back) winding too, and here the steps are a lot smaller.

We used to use voltage stabilizers on this principle, with a sliding contact, driven by a servo motor

Make break with relays is also difficult to make it work down up and also up down.

If you ever succeed, please let us know,

Success,D.

__________________
Plenty of room here
Register to Reply
Power-User

Join Date: May 2006
Location: Chennai - India
Posts: 103
#22
In reply to #11

Re: ARC Quenching - Single-Pole Double-Throw Relay

02/01/2012 2:56 AM

Is it safe to shortcircuit the winding for a short period (or long depending on how u consider 2-8ms). I thought that would cause o/p voltage to buck.

Any suggestions...

__________________
I would like to be a human in true sense one day...
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#25
In reply to #22

Re: ARC Quenching - Single-Pole Double-Throw Relay

02/01/2012 8:35 AM

Depends on what you call safe:

Relays that last a lot less than what is expected? Contacts that are burning quickly and the metal that melts down? Do the relays also stick?

I have no idea on how big the steps are and

Is a ladder safe with cut steps of 1 meter ?

Or better as example: one with at random placed steps between 5 cm and 100 cm.

Doing this properly, requires a different switching device, that controls the situation and not a gamble clicker how long it lasts system.

Switching only when the O- point is reached can help. Think of Triacs, or other electronic devices. properly controlled.

__________________
Plenty of room here
Register to Reply
Power-User

Join Date: May 2006
Location: Chennai - India
Posts: 103
#29
In reply to #25

Re: ARC Quenching - Single-Pole Double-Throw Relay

02/02/2012 2:02 AM

We are designing a triac based system for them, but they require a solution if possible, for their existing systems.

The voltage and turns in between steps are approx 30V, 25 turns...

I think the effect of shorting the windings will be visible in the o/p line. that is not a good thing..

__________________
I would like to be a human in true sense one day...
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15603
Good Answers: 982
#26
In reply to #22

Re: ARC Quenching - Single-Pole Double-Throw Relay

02/01/2012 9:24 AM

In general it is safe because of two factors. First, the voltage differential across the two contacts is relatively small. So the short circuit of connecting two transformer taps together will be a smaller voltage difference. Second, the period of time when two contacts are connected together are brief. Thus a finite number of joules will be heating this closed loop of a transformer windings, cable wiring, and two contacts. Usually this brief interval of added thermal loading will be an insignificant number of joules compared to the joules generated in normal operation.

Remember the transformer is not really an ideal voltage source. There is a source resistance of each tap winding along with the wiring and contact resistance that is connecting these two correlated voltage sources together.

Now one can certainly misapply this approach of make before break relay contacts by any of a number of bad ideas. The two that maybe relevant here are how large of a differential voltage will exist between two adjacent contacts and how frequently will these contacts be switched.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User

Join Date: May 2006
Location: Chennai - India
Posts: 103
#30
In reply to #26

Re: ARC Quenching - Single-Pole Double-Throw Relay

02/02/2012 2:06 AM

The contacts may be switched evry 200ms (worst case) and every 30 seconds (nominal condition), every 30-60 minutes (most expected), not at all (best case)..

After all is said and done, its a voltage stabiliser ;)

__________________
I would like to be a human in true sense one day...
Register to Reply
Power-User

Join Date: Apr 2007
Posts: 414
Good Answers: 19
#13

Re: ARC Quenching - Single-Pole Double-Throw Relay

02/01/2012 1:13 AM

Have you experimented with a resistor-capacitor contact protection scheme?

http://www.industrologic.com/mechrela.htm

Large high-voltage circuit breakers use oil immersion, a puff of dry air, or a pressurized Sulfur Hexafluoride atmosphere to suppress contact arcing. Those methods would also work for lower voltages and currents if the working environment gives you enough elbow room to implement them.

Register to Reply
Power-User

Join Date: May 2006
Location: Chennai - India
Posts: 103
#21
In reply to #13

Re: ARC Quenching - Single-Pole Double-Throw Relay

02/01/2012 2:54 AM

there is absolutely no room to alter anything inside the relay. I have been trying RCs. but not able to guideline a value based on my req.

__________________
I would like to be a human in true sense one day...
Register to Reply
Power-User

Join Date: May 2006
Location: Chennai - India
Posts: 103
#19

Re: ARC Quenching - Single-Pole Double-Throw Relay

02/01/2012 2:41 AM

The arcing happens on all relays. The test//analysis was done on one.

So the said relay is not a faulty relay or line, rather the arcing exists as an inherent part of the system. Our endeavour is to reduce the current transitions and also the arcing to a minimum.

__________________
I would like to be a human in true sense one day...
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#24

Re: ARC Quenching - Single-Pole Double-Throw Relay

02/01/2012 8:20 AM

I have not read all posted comments, but had past experience manufacturing voltage regulators having up to 5% regulated outputs.

What I had done was exactly the opposite of what you described. I also used multi-tapped auto-transformer type, but the tap-switching mechanism was done on the secondary side or the output side of the regulators. By doing this approach I minimized most of the arcing that otherwise will be always presented by the transformer inductive windings, and therefore prolonging the contact life of the relays.

The only time I will one relay on the primary side is when a customer put a special order to increase the range of voltage fluctuations covered, like anywhere from 130 to 270 volts range while still maintaining the 230 +/- 10% output voltage!

I believe one key advantage of my approach, switching the secondary side, since most of the relay contacts are not going to encounter pure inductive load of the transformer!

__________________
vsar
Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#27

Re: ARC Quenching - Single-Pole Double-Throw Relay

02/01/2012 12:44 PM

Have you considered "gas discharge tubes"?

When starting a compact fluorescent lamp you actually try to cause the high voltage spike that is creating your arc. For noise suppression, a capacitor is used but it sounds like you are trying to suppress the voltage spike caused by the interruption of current in an inductive circuit. The gas discharge tubes mentioned above may work out very nicely for your application. They are fairly small and cheap.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Power-User

Join Date: May 2006
Location: Chennai - India
Posts: 103
#31
In reply to #27

Re: ARC Quenching - Single-Pole Double-Throw Relay

02/02/2012 2:32 AM

Seems to be an interesting option. Will read more on them. If it seems to satisfy the requirements, will try them.

Thanks.

__________________
I would like to be a human in true sense one day...
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#28

Re: ARC Quenching - Single-Pole Double-Throw Relay

02/01/2012 2:05 PM

Vish_al210 -

To minimize contact arcings on the relay, I had done exactly the opposite of how the relays are connected as you described .

The tap changing was done on the output or load side of the transformer - not on the primary and not presenting the transformer as the load! By doing this approach I greatly minimized the magnitude of arcing caused by the transformer reactances which is mostly inductive in nature.

__________________
vsar
Register to Reply
Register to Reply 31 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

bubbapebi (2); dvmdsc (2); JRaef (1); Just an Engineer (1); kvsridhar (3); NotUrOrdinaryJoe (1); ozzb (1); PeterT (1); redfred (3); vish_al210 (14); vsar (2)