CT/PT Problems

02/03/2012 8:53 AM

Hi!

We are using 33kva supply for our factory. In the past two months we had PT failures twice and CT failure once in the metering cubicle of the electricity board. Our operations are on 50% average of contracted load. We have meggered the earthing and found values of 1 to 1.5 ohms. We have tested insulation of the XLPE cable between the pole & metering cubicle and between Metering cubicle & Isolator and found okay. The PTs and CTs have been working okay for the past three years. We are having foggy atmosphere here recently and the PTs failed even after keeping the room ventilated and heated. The failures have stretched everyone's imagination here and we are not able to pinpoint the reason for failures.

We require to know all probable reasons for failure of PTs.

We require to know all probable causes for failure of CTs.

Thanks.

Ragotham

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#1

Re: CT/PT Problems

02/03/2012 9:42 AM

Ragotham,

You can start with a few of the links on this page.

If you find nothing useful on those links try working the problem backwards.

You have had no CT/PT failures over the last thee years.

You have had multiple CT/PT failures over the past two months.

Something has obviously changed.

A good place to start your investigation would be:

The first time that the CT and/or PT was changed, was the correct replacement CT/PT used?

Were the conductors re-landed on the correct terminals?

Are the connections clean and tight?

Have you checked the wiring harness for breaks or shorts between the CT/PT's and the display(s)?

Is there a selector switch controlling how the display shows the CT/PT status? If so, check between corresponding terminals for continuity when closed/open and check tightness of conductor terminations.

Is there anything in the circuit that would cause an intermittent open across any CT/PT?

Check back with us and let us know what you find - Good Luck!

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Participant

Join Date: Apr 2011
Posts: 3
#2

Re: CT/PT Problems

02/04/2012 7:08 AM

Dear RAGOTHAM,

There are different reason for C.T.and P.T. failure. System high voltage and spike in the system is the common cause for C.T. and P.T. failure.Following are the posibilties for failure of C.T.and P.T.

1) Open secondary circuit or became high resistive.(for C.T. only)

2) Internal insulation failure due to aging or degradation of insulating oil or paper.

3) Ferro-resonance in the system.

4) Improper creepage distance of the insulator.

5) Higher harmonic level in the system.

RAKHOLIA B.K.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Aug 2008
Posts: 15
#3
In reply to #2

Re: CT/PT Problems

02/08/2012 9:00 AM

Dear Mr.BKR,

do you mean insulating oil or paper in the transformer?

We have many AC motors on VFDs, SCR controlled heaters, etc.. Is harmonics filters the solution, if so how to specify?

I also wish to inform you that on the same EB feeder there has been PT and CT failures at 4 more consumers factories.

Thanks

Ragotham

Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#4
In reply to #3

Re: CT/PT Problems

02/10/2012 2:34 AM

Dear Ragotham,

Due to operation of many AC Drives and SCR controlled heaters and other non-linear electrical loads, definitely the power system pollution level increases beyond acceptable /normal level and which may cause ferro-resonance effect and abnormal heating effect in CTs and PTs. This issue must be solved immediately by proper harmonic study of the existing power system and installation of harmonic suppressor reactors, harmonic filters etc.This will prevent further damage of CTs,PTs and other costly electrical equipments. Hiring of electrical consultant in this specialised field is suggested to do the above work.

Manindra

__________________
Manindra
Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

BKR (1); KJK/USA (1); manindra (1); ragotham (1)

Previous in Forum: What are the Causes/Reasons for 15th Harmonic Occurrence   Next in Forum: Thermal Overload Relay

Advertisement