Thermal Overload Relay

02/03/2012 10:19 AM

What should be correct setting of thermal overload relay?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Thermal Overload Relay

02/03/2012 10:33 AM

Before damage is done...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Thermal Overload Relay

02/03/2012 10:52 AM

It should be set at a point that protects the equipment from thermal damage.

I"d consult with the maker of the device you want to protect. I'm having trouble divining the make and model number to give to the manufacturer, you'll have to do that.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3

Re: Thermal Overload Relay

02/03/2012 11:00 AM

In a DOL starter, i would set it at the rated full load current of the motor.

In a ΥΔ starter, IF THE RELAY IS WITHIN THE Δ, i would set it to to the FLA/√3 = 58.3% of the full load current of the motor.

This is what i would do.

Up to you what you want to do....

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4
In reply to #3

Re: Thermal Overload Relay

02/03/2012 11:55 AM

Generally true, but as pointed out, we don't know the mfr name and model. Some (most) require setting at nameplate FLC and the pickup point is already factored in, others require the user to factor in the pickup point from the nameplate FLC and set the trip point there. You don't know until you RTFM. (Read The F###ing Manual)

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#5
In reply to #3

Re: Thermal Overload Relay

02/03/2012 12:06 PM

I'll give you a GA because most of the questions here relate to starters and motor drives. Just because the OP doesn't know what they want doesn't mean you cannot provide a valid response.

Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#6
In reply to #5

Re: Thermal Overload Relay

02/03/2012 2:47 PM

"Just because the OP doesn't know what they want doesn't mean you cannot provide a valid response."

It appears to me that you have never been dragged into court by someone who couldn't communicate clearly what they wanted or needed, but you provided information that seemed appropriate for the application anyway. The individual (foolishly) acted on what is now known to be inappropriate advice and suffered a subsequent loss.

... not that I am bitter or anything.

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7
In reply to #3

Re: Thermal Overload Relay

02/03/2012 10:27 PM

Ooops. Calculation error. 1/√3 = 57.7%

Some expansion on the answer, taking into account the more recent responses....

i assumed you are from India, so i referred to the practice here. If you are not from India, then service factor may be involved, and my response may not be appropriate.

If you are located in India, you may need to find the actual full load current of the motor, which may be somewhat different from the nameplate data. You need to set the relay to the actual current. You may end up with nuisance trips otherwise.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Jul 2007
Posts: 26
Good Answers: 1
#8
In reply to #7

Re: Thermal Overload Relay

02/03/2012 10:53 PM

There are different opinions to set the over load relay .Normally 105% is recommended considering the service factor , 5 % more than the FLC to meet the load fluctuations. But I do the following :

Set it at 105 % and if the machine is running in perfect load conditions , measure the actual load current . Then if the current drawn is less than FLC , then I change the OLR setting to 105 % of the actual current drawn . This way you are protecting the motor for any over load above the normal current at the time of commissioning . Also this will help to monitor the deterioration of the conditions of the drive , in case unexpected overload gets reflected on the motor. From this you can finalise the OLR setting . At any cost don't cross 105% of the FLC.

Register to Reply Score 1 for Good Answer
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#9
In reply to #8

Re: Thermal Overload Relay

02/03/2012 11:34 PM

IEC relays already have the 1.05 factor built in. In other words, if one sets an IEC relay at 10A, it will (a) not trip at 10.5A and (b) will definitely trip at 12A. So, designers target 1.125 as the aymptotic ordinate.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#12
In reply to #7

Re: Thermal Overload Relay

02/10/2012 2:43 AM

Before setting the O/L relay motor FLA must be checked carefully( not depending on Name plate data only).

Manindra

__________________
Manindra
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#13
In reply to #12

Re: Thermal Overload Relay

02/10/2012 4:42 AM

i said this in #7 : If you are located in India, you may need to find the actual full load current of the motor, which may be somewhat different from the nameplate data. You need to set the relay to the actual current. You may end up with nuisance trips otherwise.

What you are now saying in response to my post...is it something different?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#10

Re: Thermal Overload Relay

02/04/2012 6:17 PM

Per NEC (Article 430.32 A)

This overload device shall be selected to trip or shall be rated at no more than the following percent of the motor nameplate full-load current rating:

Motors with a marked service factor 1.15 or greater 125%

Motors with a marked temperature rise 40°C or less 125%

All other motors 115%

In some cases, it may be (Article 430.32 C):

Motors with marked service factor 1.15 or greater 140%

Motors with a marked temperature rise 40°C or less 140%

All other motors 130%

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Member

Join Date: Feb 2012
Posts: 5
#11

Re: Thermal Overload Relay

02/05/2012 10:13 AM

85 % of KW for example 5 KW motor thermal over load setting is 8.5 A

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#14

Re: Thermal Overload Relay

02/13/2012 10:48 PM

Sir,

Many answers...all helpful. Let's step back a second:

The thermal overload relay is attempting to mimic or approximate the thermal conditions within the winding of the motor and cause the power to be shut off before the winding temperature exceeds that at which the insulation of the windings is damaged or destroyed. Over many years, the accumulated experience of engineers, designers, users, insurers, etc. have resulted in the rules quoted in the many answers.

You will see that motor designs which include a higher load tolerance (higher temperature insulation and higher service factors) allow a higher thermal overload relay setting. No one mentioned that if the motor and the controller are in different locations and the temperature difference between these locations is significant then the thermal overload relay will have to be set lower or higher according to that difference between the local temperatures. Also, some design's of thermal overload relays will respond quickly to single-phase conditions while the motor is running (and also respond to very unbalanced currents due to voltage imbalance), while other designs will not, (A single-phased motor, if lightly loaded will often draw less current than its nameplate, but will still burn-up because of the excessive heating caused by the imbalanced magnetic currents within the motor.)

Go to the codes or regulations adopted by your local authority. If there is none, then the NEC (National Electrical Code in the USA), article 430, will be a good starting point because it has over 100 years of experience to guide its rules.

Finally, remember that a thermal overload relay is only a good guess at the actual motor's temperature. The best approach (required on large motors) is a sensor embedded within the winding, which is used to interrupt current if/when the winding gets too hot.

--John M.

Register to Reply
Register to Reply 14 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

cuba_pete (1); Doorman (1); jmueller (1); JRaef (1); kvsridhar (4); lyn (1); manindra (1); msamad (1); niazi677 (1); SolarEagle (1); Voltamps (1)